Technically it’s is a porte-cochere. The AHJ is not requiring protection, the engineer is.
David Autry Meininger Fire Protection 2521 West L Street, Suite 5 Lincoln, NE 68522 402.466.2616 402.466.2617 fax [email protected] *From:* Sprinklerforum [mailto: [email protected]] *On Behalf Of *Travis Allen- Allen Engineering *Sent:* Friday, March 03, 2017 10:55 AM *To:* [email protected] *Subject:* RE: Canopy Is it a canopy or porte-cochere where vehicles enter or leave? IBC CANOPY definition: A structure, enclosure or shelter constructed of fabric or pliable materials supported by any manner, except by air or the contents it protects, and is open without sidewalls or drops on 75 percent or more of the perimeter. AHJ’s often require porte-cochere's to be sprinklered (even if detached) due to the higher hazard of fueled vehicles. Many jurisdictions amend their codes to limit the size of canopies that don't require sprinkler protection, as well. Travis E. Allen, PE Principal Allen Engineering, PLLC *From:* David Autry [mailto:[email protected] <[email protected]>] *Sent:* Friday, March 3, 2017 7:37 AM *To:* [email protected] *Subject:* Canopy I’ve got a 4 story Hotel with a detached Canopy. V-A Construction type protected NFPA 13 (2013), R-1 occupancy. The Canopy is of non-combustible construction and detached from the building. I have an Engineer telling me I need to protect this structure. Am I missing something? 2006 IBC, Building code. Thanks, David Autry Meininger Fire Protection 2521 West L Street, Suite 5 Lincoln, NE 68522 402.466.2616 402.466.2617 fax [email protected]