Technically it’s is a porte-cochere. The AHJ is not requiring protection,
the engineer is.



David Autry



Meininger Fire Protection

2521 West L Street, Suite 5

Lincoln, NE 68522

402.466.2616

402.466.2617 fax

[email protected]



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Travis
Allen- Allen Engineering
*Sent:* Friday, March 03, 2017 10:55 AM
*To:* [email protected]
*Subject:* RE: Canopy



Is it a canopy or porte-cochere where vehicles enter or leave? IBC CANOPY
definition: A structure, enclosure or shelter constructed of fabric or
pliable materials supported by any manner, except by air or the contents it
protects, and is open without sidewalls or drops on 75 percent or more of
the perimeter.



AHJ’s often require porte-cochere's to be sprinklered (even if detached)
due to the higher hazard of fueled vehicles. Many jurisdictions amend their
codes to limit the size of canopies that don't require sprinkler
protection, as well.



Travis E. Allen, PE

Principal



Allen Engineering, PLLC



*From:* David Autry [mailto:[email protected] <[email protected]>]
*Sent:* Friday, March 3, 2017 7:37 AM
*To:* [email protected]
*Subject:* Canopy



I’ve got a 4 story Hotel with a detached Canopy.

V-A Construction type protected NFPA 13 (2013), R-1 occupancy.

The Canopy is of non-combustible construction and detached from the
building. I have an Engineer telling me I need to protect this structure.
Am I missing something?

2006 IBC, Building code.



Thanks,



David Autry



Meininger Fire Protection

2521 West L Street, Suite 5

Lincoln, NE 68522

402.466.2616

402.466.2617 fax

[email protected]