If less than 2 in 12 then it's flat, not sloped.

On Tue, Mar 7, 2017 at 8:19 AM, Brian Harris <[email protected]>
wrote:

> If memory serves me correctly you can slope uphill if the pitch does not
> exceed 2:12
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssytemsinc.com <http://bvssystemsinc.com/>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Travis Mack, SET
> *Sent:* Tuesday, March 07, 2017 11:18 AM
> *To:* [email protected]
> *Subject:* Re: Cabinets Against a Wall
>
>
>
> I always thought it was cross slope and down, but never up.  Has that
> changed?
>
> Travis Mack, SET
>
> MFP Design, LLC
>
> 2508 E Lodgepole Drive
>
> Gilbert, AZ 85298
>
> 480-505-9271 <(480)%20505-9271>
>
> fax: 866-430-6107 <(866)%20430-6107>
>
> email:[email protected]
>
>
>
> http://www.mfpdesign.com
>
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> LinkedIn: https://www.linkedin.com/in/travismack
>
> On 3/7/2017 9:17 AM, Steve Leyton wrote:
>
> I didn’t get that impression at all, so perhaps it’s still a little too
> obscure.  Is it the intent that residential sidewalls can be arranged so
> they discharge cross-slope and up-slope?  I don’t think so …
>
>
>
> SML
>
>
>
>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Matt
> Grise
> *Sent:* Tuesday, March 07, 2017 8:11 AM
> *To:* [email protected]
> *Subject:* RE: Cabinets Against a Wall
>
>
>
> Steve,
>
>
>
> I got the impression NFPA13d 2016 8.1.1 was meant to deal with both
> pendant and sidewall sprinklers. The picture shows only pendants, but it is
> in a section separate from the pendant/sidewall positioning sections.
> Section 10.2 also makes several references to general and sidewall spacing
> under slopes.
>
>
>
> Also – the tyco listings previously had multiple diagrams showing how to
> position residential sidewalls under sloped ceilings. Those were removed
> after the 13R/D code language was changed to the generalized description of
> heads under slopes.
>
>
>
> Matt
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Steve
> Leyton
> *Sent:* Tuesday, March 07, 2017 9:44 AM
> *To:* [email protected]
> *Subject:* RE: Cabinets Against a Wall
>
>
>
> Sloped ceiling?   Can a sidewall be oriented so it discharges down-slope?
>
>
>
> You comment sent me scurrying to our tech data library and also to NFPA
> 13D and 13.  Both standards are mute regarding the positioning of
> residential horizontal sidewall sprinklers on/under sloped ceilings.
> Viking tech data sheets say to refer to the appropriate standard.  Tyco
> says their RHSW sprinklers can be used under sloped ceilings but no
> specific positioning criteria is offered.   If we use the spray sprinkler
> criteria, the sprinklers have to be oriented so they are placed at the peak
> of a sloped ceiling and spray downward.
>
>
>
> Am I missing something somewhere regarding RHSW sprinklers and sloped
> ceilings?
>
> Steve L.
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Richard
> Mote
> *Sent:* Tuesday, March 07, 2017 6:18 AM
> *To:* [email protected]
> *Subject:* RE: Cabinets Against a Wall
>
>
>
> This a sloped ceiling area, with the ceiling being attached directly to
> the underside of the joists. No space to run pendants in a conditioned area.
>
>
>
> *Richard Mote*
>
> Design Manager
>
> [image: http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg]
>
> *P:* 570.837.7647 <(570)%20837-7647>  ·  *W:* 877.324.ROWE  ·  *F:*
> 570.837.6335 <(570)%20837-6335>
>
> PO Box 407 · 7993 US Route 522, Suite 1 · Middleburg, PA 17842
>
> *RoweSprinkler.com  *·  [email protected]
>
>
>
> *** Confidentiality Notice ***
>
> This email and any attachments thereto may contain information that is
> privileged and confidential and is intended only for the use of the
> addressee. If the reader of the message is not the intended recipient or an
> authorized representative of the intended recipient, you are hereby
> notified that any dissemination of this communication is strictly
> prohibited. If you have received this communication in error, please notify
> us immediately by e-mail at *[email protected]
> <[email protected]>* or by telephone at *570-837-7647
> <(570)%20837-7647>* and delete the message and any attachments
> permanently from your system.
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Matt
> Grise
> *Sent:* Tuesday, March 07, 2017 8:56 AM
> *To:* [email protected]
> *Subject:* RE: Cabinets Against a Wall
>
>
>
> Pendant sprinkler?
>
>
>
> Matt
>
>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Richard
> Mote
> *Sent:* Tuesday, March 07, 2017 7:50 AM
> *To:* [email protected]
> *Subject:* Cabinets Against a Wall
>
>
>
> NFPA 13D, 2017 (the edition currently in force in PA) 8.2.5.6.3 Where
> sidewall sprinklers are more than 3 ft. above the top of cabinets, the
> sprinkler shall be permitted to be installed on the wall above the cabinets
> where the cabinets are no greater than 12 in. from the wall.
>
>
>
> We have a case that meets all of the above criteria except for a 2” wide
> crown molding around the top of the cabinets, so the overall width is 14”
> around the top of the cabinet. Obvious solution is put the sprinkler on the
> other end of the room, however that wall is a rated wall with a
> un-conditioned space on the other side.
>
> Any sugestions?
>
>
>
>
>
> *Richard Mote*
>
> Design Manager
>
> [image: http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg]
>
> *P:* 570.837.7647 <(570)%20837-7647>  ·  *W:* 877.324.ROWE  ·  *F:*
> 570.837.6335 <(570)%20837-6335>
>
> PO Box 407 · 7993 US Route 522, Suite 1 · Middleburg, PA 17842
>
> *RoweSprinkler.com  *·  [email protected]
>
>
>
> *** Confidentiality Notice ***
>
> This email and any attachments thereto may contain information that is
> privileged and confidential and is intended only for the use of the
> addressee. If the reader of the message is not the intended recipient or an
> authorized representative of the intended recipient, you are hereby
> notified that any dissemination of this communication is strictly
> prohibited. If you have received this communication in error, please notify
> us immediately by e-mail at *[email protected]
> <[email protected]>* or by telephone at *570-837-7647
> <(570)%20837-7647>* and delete the message and any attachments
> permanently from your system.
>
>
>
>
>
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>


-- 
Ron Greenman

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to