I'm wondering the same thing Art.  Even if you need the pump, go to a 2000
gpm pump at less psi to keep under 175 at churn.

 

Cliff Whitfield, SET

President

 

Fire Design, Inc.

184 Comfort Place

Burnsville, NC 28714

Ph: 828-284-4772

 



 

 <mailto:[email protected]> [email protected]

 <http://www.fire-design.com/> www.fire-design.com

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Art Tiroly
Sent: Thursday, April 6, 2017 5:06 PM
To: [email protected]
Subject: RE: NFPA 20 4.7.7.2 

 

The LP-46 only requires 15-20 psi end head.

I don't understand the excessive pressure you require.

The 58/56/1583 is a great suction source.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Prahl, Craig/GVL
Sent: Thursday, April 06, 2017 4:52 PM
To: [email protected]
Subject: RE: NFPA 20 4.7.7.2 

 

You can't use the PRV to relieve excess pressure under normal conditions due
to an over designed pump.  There can be unexpected times in a municipal
supply where pressure spikes occur for various reasons.  If your pump
selection puts you close to the maximum system working pressure under normal
conditions and a spike in the supply were to occur, with no means of relief,
downstream system damage could occur.  

 

 

One other concern over this selection is that it is a 1500 gpm pump with
only a 1583 gpm tested source flow rate.  The pump may not be capable of
reaching the 150 % mark unless you know if the municipal supply can actually
provide more than 1583 gpm.  Not knowing the actual system demands makes it
difficult to address this issue any farther.

 

 

 

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected] <mailto:[email protected]> 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Tom Duross
Sent: Thursday, April 06, 2017 4:34 PM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: NFPA 20 4.7.7.2 [EXTERNAL]

 

Looks like you could be above 200 PSI churn or system pressure.  The
standard (2013 referenced) does not allow you to use the relief as a means
of blowing off excess pressure above 175.

Tom

 

Is the 140 psi total pressure or pump rating?

 

The pressure relief valve comes into play if the combination of supply
pressure and pump pressure exceeds the allowable system pressure, which for
most cases is 175 psi.

 

So if you had fluctuating supply pressures, during a higher than normal
pressure event, the system could relieve and not damage your downstream, 175
psi rated system.

 

Is this a diesel or electric?

 

How much pressure do you need at these heads?

 


Craig L. Prahl 

 

Hi Forum , 

 

Could someone shed some light on the requirements for 4.7.7.2  .   I have a
project where the quoted fire pump comes with a Pressure relief valve and
waste cone . 

 

City pressure is 58/56/1586  ,  we are using a 1500gpm pump at 140 psi to
get the flow and pressure we need to supply a freezer using LP-46 heads .  I
find many references to the use of Pressure relief valves being 

Used but 4.7.7.2 is  causing me to scratch my head . 

 

 

Colin 

 

 

 

 

 

 


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campai
gn=sig-email&utm_content=emailclient&utm_term=icon> 

Virus-free.
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campai
gn=sig-email&utm_content=emailclient&utm_term=link> www.avast.com 

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to