A.8.15.7.5  Short-term transient storage, such as that for delivered
packages, and the presence of planters, newspaper machines, and so forth,
should not be considered for storage or handling of combustibles. *** The
presence of combustible furniture on balconies for occupant use should not
require sprinkler protection.***

On Mon, Apr 17, 2017 at 7:54 AM, Steve Leyton <[email protected]>
wrote:

> John:
>
> I was responding earlier from home and now, seated at my incredibly
> cluttered desk, have reviewed 8.15.7 (2013 ed.).   As tactfully as I can
> say this, you’re reaching.  For very hard-to-grasp fruit.   I sincerely
> doubt you’re going to get any fire or building official to see your way to
> applying an exception that describes a non-combustible envelope with wood
> framing and sprinklered interstitial spaces to a vinyl or nylon canopy.
>
>
>
> In reality – and I’ve had to walk this line hundreds of times here in fair
> weather California – the underlying reason that you’re in pickle and the
> owner wants to exclude sprinklers is because they don’t want to deal with
> the trouble and expense of designing a canopy frame that will withstand the
> weight of its cover, water-filled sprinkler pipe and wind shear.  Out here,
> you can add the applied horizontal force of seismic bracing as well.    In
> cold weather climates, there’s the challenge of having to make the system
> dry, but often al fresco dining areas are built like screen rooms with hard
> framing above and around, but that’s a different story.
>
>
>
> Apologies for shamelessly pimping my business model, but if the architect
> and owner had been indoctrinated (inoculated) regarding the need to
> sprinkler such spaces early in the project (like, DESIGN PHASE), you
> wouldn’t inherit this interpretive challenge that puts you at risk
> financially.    One of the reasons I don’t miss contracting is that as a
> consultant, I’m not put in the unenviable and uncomfortable position of
> lobbying against sprinklers.  Why wouldn’t we (proactive industry types)
> want to protect areas where people are eating and drinking, and especially
> where they are potentially drinking alcoholic beverages, by candlelight and
> in some states still, smoking?
>
>
>
> Steve L.
>
>
>
>
>
>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Steve Leyton
> *Sent:* Monday, April 17, 2017 6:16 AM
>
> *To:* [email protected]
> *Subject:* RE: Covered Restaurant Seating Area
>
>
>
> I suggest you run those by your local building and fire officials.
>
>
>
>
>
> Steve
>
>
>
>
>
> -------- Original message --------
>
> From: John Irwin <[email protected]>
>
> Date: 4/17/17 6:00 AM (GMT-08:00)
>
> To: [email protected]
>
> Subject: RE: Covered Restaurant Seating Area
>
>
>
> I would disagree with this unless you can direct me to some more
> information. 8.15.7.3(2) even goes on to spell out Light and Ordinary
> Hazard Occupancy situations where sprinklers can be omitted.
>
>
>
> *John Irwin - CET*
>
> *Division Manager – Fire Sprinklers*
>
> *Critical System Solutions, LLC*
>
>
> *Licence Number: FPC16-000053 *Cell:     813.618.2781 <(813)%20618-2781>
>
> Email:  [email protected]
>
>
>
> [image: certifiedmark300 - small]
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Steve
> Leyton
> *Sent:* Monday, April 17, 2017 8:53 AM
> *To:* [email protected]
> *Subject:* RE: Covered Restaurant Seating Area
>
>
>
> Overhang exceptions only apply when the area below is not used for storage
> or handling of combustibles or otherwise classified as occupied by the
> applicable building code or building official. As Spicey would say,
> restaurant seating areas are assembly occupancy, PERIOD!
>
>
>
>
>
> Steve
>
>
>
>
>
> -------- Original message --------
>
> From: John Irwin <[email protected]>
>
> Date: 4/17/17 5:45 AM (GMT-08:00)
>
> To: [email protected]
>
> Subject: RE: Covered Restaurant Seating Area
>
>
>
> I’m using 13 8.15.7 to argue that if the fabric covering the steel frame
> is non-combustible than perhaps the sprinklers are not required.
>
>
>
>
>
> *John Irwin - CET*
>
> *Division Manager – Fire Sprinklers*
>
> *Critical System Solutions, LLC*
>
>
> *Licence Number: FPC16-000053 *Cell:     813.618.2781 <(813)%20618-2781>
>
> Email:  [email protected]
>
>
>
> [image: certifiedmark300 - small]
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Steve
> Leyton
> *Sent:* Monday, April 17, 2017 8:33 AM
> *To:* [email protected]
> *Subject:* RE: Covered Restaurant Seating Area
>
>
>
> Often, we try to read the standards backwards. The way that NFPA 13 is
> written, it requires sprinklers everywhere. What the client is hopeful of
> is an exception but I'm pretty sure they are not going to find one for this
> particular application.  If I'm taking the contrary point of view, I would
> say that instead of looking for a section  that requires sprinklers here or
> there,  show me where it says I don't have to put sprinklers over this
> occupied area that is part of the use of the protected premises.
>
>
>
>
>
> Steve Leyton
>
>
>
>
>
>
>
>
>
> -------- Original message --------
>
> From: John Irwin <[email protected]>
>
> Date: 4/17/17 4:11 AM (GMT-08:00)
>
> To: [email protected]
>
> Subject: Covered Restaurant Seating Area
>
>
>
> Here’s the situation. Existing restaurant seating area covered by steel
> frame and vinyl or nylon tarp. 100% open. Protected with sprinklers.
>
>
>
> Additional covered seating area being added that will be steel frame but
> insulated aluminum panel roof. 100% open.
>
>
>
> Client doesn’t believe sprinklers are required and wants the existing
> sprinklers under the vinyl canopy removed.
>
>
>
> Can someone direct me to code references?
>
>
>
>
>
> *John Irwin*
>
> *Division Manager – Fire Sprinklers *
>
> *Critical System Solutions, LLC*
>
>
> *License Number: FPC16-000053 *2830 Scherer Drive, Suite 300
> St. Petersburg, FL  33716
> Office: 727.209.5122 <(727)%20209-5122>
>
> Fax:      727.209.5126 <(727)%20209-5126>
>
> Cell:     813.618.2781 <(813)%20618-2781>
>
> Email:  [email protected]
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to