What does 8.15.7.5 say? “Sprinklers SHALL be installed under exterior protections greater than 2’ wide over areas where combustibles are stored. By any reasonable assessment, the configuration of a restaurant seating area would have combustibles in place (i.e. stored) as a function of its normal use and occupancy, wouldn’t you agree? Citing the furniture exception in the annex for (residential) balconies seems a bit of a stretch, no?
SML From: Sprinklerforum [mailto:[email protected]] On Behalf Of IPA Sent: Monday, April 17, 2017 8:41 AM To: [email protected] Subject: Re: Covered Restaurant Seating Area A.8.15.7.5 Short-term transient storage, such as that for delivered packages, and the presence of planters, newspaper machines, and so forth, should not be considered for storage or handling of combustibles. *** The presence of combustible furniture on balconies for occupant use should not require sprinkler protection.*** On Mon, Apr 17, 2017 at 7:54 AM, Steve Leyton <[email protected]<mailto:[email protected]>> wrote: John: I was responding earlier from home and now, seated at my incredibly cluttered desk, have reviewed 8.15.7 (2013 ed.). As tactfully as I can say this, you’re reaching. For very hard-to-grasp fruit. I sincerely doubt you’re going to get any fire or building official to see your way to applying an exception that describes a non-combustible envelope with wood framing and sprinklered interstitial spaces to a vinyl or nylon canopy. In reality – and I’ve had to walk this line hundreds of times here in fair weather California – the underlying reason that you’re in pickle and the owner wants to exclude sprinklers is because they don’t want to deal with the trouble and expense of designing a canopy frame that will withstand the weight of its cover, water-filled sprinkler pipe and wind shear. Out here, you can add the applied horizontal force of seismic bracing as well. In cold weather climates, there’s the challenge of having to make the system dry, but often al fresco dining areas are built like screen rooms with hard framing above and around, but that’s a different story. Apologies for shamelessly pimping my business model, but if the architect and owner had been indoctrinated (inoculated) regarding the need to sprinkler such spaces early in the project (like, DESIGN PHASE), you wouldn’t inherit this interpretive challenge that puts you at risk financially. One of the reasons I don’t miss contracting is that as a consultant, I’m not put in the unenviable and uncomfortable position of lobbying against sprinklers. Why wouldn’t we (proactive industry types) want to protect areas where people are eating and drinking, and especially where they are potentially drinking alcoholic beverages, by candlelight and in some states still, smoking? Steve L. From: Sprinklerforum [mailto:[email protected]<mailto:[email protected]>] On Behalf Of Steve Leyton Sent: Monday, April 17, 2017 6:16 AM To: [email protected]<mailto:[email protected]> Subject: RE: Covered Restaurant Seating Area I suggest you run those by your local building and fire officials. Steve -------- Original message -------- From: John Irwin <[email protected]<mailto:[email protected]>> Date: 4/17/17 6:00 AM (GMT-08:00) To: [email protected]<mailto:[email protected]> Subject: RE: Covered Restaurant Seating Area I would disagree with this unless you can direct me to some more information. 8.15.7.3(2) even goes on to spell out Light and Ordinary Hazard Occupancy situations where sprinklers can be omitted. John Irwin - CET Division Manager – Fire Sprinklers Critical System Solutions, LLC Licence Number: FPC16-000053 Cell: 813.618.2781<tel:(813)%20618-2781> Email: [email protected]<mailto:[email protected]> [certifiedmark300 - small] From: Sprinklerforum [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Monday, April 17, 2017 8:53 AM To: [email protected]<mailto:[email protected]> Subject: RE: Covered Restaurant Seating Area Overhang exceptions only apply when the area below is not used for storage or handling of combustibles or otherwise classified as occupied by the applicable building code or building official. As Spicey would say, restaurant seating areas are assembly occupancy, PERIOD! Steve -------- Original message -------- From: John Irwin <[email protected]<mailto:[email protected]>> Date: 4/17/17 5:45 AM (GMT-08:00) To: [email protected]<mailto:[email protected]> Subject: RE: Covered Restaurant Seating Area I’m using 13 8.15.7 to argue that if the fabric covering the steel frame is non-combustible than perhaps the sprinklers are not required. [cid:[email protected]] John Irwin - CET Division Manager – Fire Sprinklers Critical System Solutions, LLC Licence Number: FPC16-000053 Cell: 813.618.2781<tel:(813)%20618-2781> Email: [email protected]<mailto:[email protected]> [certifiedmark300 - small] From: Sprinklerforum [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Monday, April 17, 2017 8:33 AM To: [email protected]<mailto:[email protected]> Subject: RE: Covered Restaurant Seating Area Often, we try to read the standards backwards. The way that NFPA 13 is written, it requires sprinklers everywhere. What the client is hopeful of is an exception but I'm pretty sure they are not going to find one for this particular application. If I'm taking the contrary point of view, I would say that instead of looking for a section that requires sprinklers here or there, show me where it says I don't have to put sprinklers over this occupied area that is part of the use of the protected premises. Steve Leyton -------- Original message -------- From: John Irwin <[email protected]<mailto:[email protected]>> Date: 4/17/17 4:11 AM (GMT-08:00) To: [email protected]<mailto:[email protected]> Subject: Covered Restaurant Seating Area Here’s the situation. Existing restaurant seating area covered by steel frame and vinyl or nylon tarp. 100% open. Protected with sprinklers. Additional covered seating area being added that will be steel frame but insulated aluminum panel roof. 100% open. Client doesn’t believe sprinklers are required and wants the existing sprinklers under the vinyl canopy removed. Can someone direct me to code references? John Irwin Division Manager – Fire Sprinklers Critical System Solutions, LLC License Number: FPC16-000053 2830 Scherer Drive, Suite 300 St. Petersburg, FL 33716 Office: 727.209.5122<tel:(727)%20209-5122> Fax: 727.209.5126<tel:(727)%20209-5126> Cell: 813.618.2781<tel:(813)%20618-2781> Email: [email protected]<mailto:[email protected]> _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org