You have 3 options,
Thrust block
Mega lug type
Rod back to fitting.


Sent from my T-Mobile 4G LTE Device


-------- Original message --------
From: "Smith, David" <[email protected]>
Date: 4/26/17 6:52 PM (GMT-05:00)
To: [email protected]
Subject: In Building Riser -- Restraints

Quick question came up recently on the 1 piece in building risers. Typically we 
have seen contractors provide thrust blocks at the bend. We’ve had one 
installed recently without one and the foundation was poured before we were 
able to view it. The contractor is advising us that a thrust block is not 
needed. The specification sheet provided advises:

If the piping installation is essentially complete, the piping
restraints may adequately take the thrust loads generated by
having a blind end on the pipe system. In these cases, no
special actions to restrain thrust or side loads are required,
and the fitting installed in the system may be adequate for
hydrostatic testing.

Is the restraint at the pipe connection on the supply side all that is needed?


[CityofLO_Seal_OptSiz#E2D662 (3)]David Smith | Deputy Fire Marshal
P 503.635.0378 | F 503.635.0376
[email protected]<mailto:[email protected]>
300 B Avenue | PO BOX 369 Lake Oswego OR 97034

PUBLIC RECORDS LAW DISCLOSURE This e-mail is a public record of the City of 
Lake Oswego and is subject to public disclosure unless exempt from disclosure 
under Oregon Public Records Law. This email is subject to the State Retention 
Schedule.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to