Shawn,
It might be worth asking the people at Ames/Watts why they provide
rodding brackets on the device if that's an unacceptable method of joint
restraint. I'd be interested in the answer.
sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 04/27/2017 7:43 AM, Shawn Chapman wrote:
Ames/Watts will NOT go on record to allow it without a thrust block @ the turn
up elbow. Practicality?? to rod back, but no document to allow. Just went
through the same scenario.
-----Original Message-----
From: Smith, David <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Wed, Apr 26, 2017 7:18 pm
Subject: RE: In Building Riser -- Restraints
Great, thanks! This was actually the first time we had it come up on the 1
piece riser. I’m assuming the other underground contractors simply poured a
thrust block because it was either habit or easier than educating us…
David Smith | DeputyFire Marshal
P 503.635.0378 | F 503.635.0376
[email protected]
300 B Avenue | PO BOX 369 Lake Oswego OR 97034
From: Sprinklerforum [mailto:[email protected]]On
Behalf Of Richard Carr
Sent: Wednesday, April 26, 2017 4:00 PM
To: [email protected]
Subject: RE: In Building Riser -- Restraints
You have 3 options,
Thrust block
Mega lug type
Rod back to fitting.
Sent from my T-Mobile 4G LTE Device
-------- Original message --------
From: "Smith, David" <[email protected]>
Date: 4/26/17 6:52 PM (GMT-05:00)
To: [email protected]
Subject: In Building Riser -- Restraints
Quick question came up recently on the 1 piece in building risers. Typically we
have seen contractors provide thrust blocks at the bend. We’ve had one
installed recently without one and the foundation was poured before we were
able to view it. The contractor is advising us that a thrust block is not
needed. The specification sheet provided advises:
If the piping installation is essentially complete, the piping
restraints may adequately take the thrust loads generated by
having a blind end on the pipe system. In these cases, no
special actions to restrain thrust or side loads are required,
and the fitting installed in the system may be adequate for
hydrostatic testing.
Is the restraint at the pipe connection on the supply side all that is needed?
David Smith | DeputyFire Marshal
P 503.635.0378 | F 503.635.0376
[email protected]
300 B Avenue | PO BOX 369 Lake Oswego OR 97034
PUBLIC RECORDS LAW DISCLOSURE This e-mail is a public record of the City of
Lake Oswego and is subject to public disclosure unless exempt from disclosure
under Oregon Public Records Law. This email is subject to the State Retention
Schedule.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org