Jeff, my experience has been the same.
Thank you, Bob Knight, CET III 208-318-3057 From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jeff Normand Sent: Monday, May 22, 2017 3:21 PM To: [email protected]; [email protected] Subject: Re: Hose Valve Location I'm thinking it says a hose valve at every required stairwell. Since this stair does not have access then it would not be a required stairway. Therefore hose valve not required. I have run into this before on a high rise with 3 stairs on the lower 8 levels and 2 stairs on upper levels. One of the stairs did not have access on the lower 8 floors, therefore no hose valve. Jeff On Mon, May 22, 2017 at 12:50 PM, Bob <[email protected]> wrote: I have a stairway that has no access to the 1st floor, but it does exit to the outside of building. The ANNEX material shows a hose valve located with respect to the floor access, since there is no floor access would the hose valve be required for this level? Thank you, Bob Knight, CET III 208-318-3057 FBK-LOGO-SMALL _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org