An inadequate system is usually treated as no system, so quantities for 
unsprinklered facilities would be allowed. Ran into this with a pool supply 
store with an OH2 system. They could only store as much Class III oxydizers as 
the could in an unsprinklered facility.   
    
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (ofc)
  
860-553-3553 (fax)
  
860-608-4559 (cell)
  
  
  
  
  

  
  
>   
> On May 23, 2017 at 7:04 PM,  <James Crawford 
> (mailto:[email protected])>  wrote:
>   
>   
>         
>   
>
> NFPA #30    (2008 ed)
>
>   
>
>   
>
>   
>
> We have a client that has a Liquid warehouse (1,200 ft²) that did not require 
> sprinkler protection by code, but did require sprinkler protection by the AHJ 
> to get a building permit. The system is an Ordinary hazard group 2 dry system.
>
>   
>
>   
>
>   
>
> They store class II and IIIB liquids in steel drums and Plastic IBC, 
> originally storage was on the floor to 4’-0” one drum or tote high.
>
>   
>
>   
>
>   
>
> But as with all thing the company grows and they want to store higher.
>
>   
>
>   
>
>   
>
> Table 12.6.2.2 Quantity Limitations for unprotected Liquid Warehouses will 
> allow 10’-0” of class II and 15’-0” of class IIIB
>
>   
>
>   
>
>   
>
> So my understanding is that unprotected is defined as not protected to NFPA 
> #30, so based on Table 12.6.2.2 they can store these products to the heights 
> noted even thou the area is sprinkled to NFPA #13 Ordinary hazard group 2.
>
>   
>
>   
>
>   
>
> Am I missing something?
>
>   
>
>   
>
>   
>
>   
>
>   
>
> Thank you
>
>   
>
>   
>
>   
>
>   
>
>   
>
> James Crawford
>
>   
>
> Phaser Fire Protection Ltd.
>
>   
>
> Phone    604-888-0318
>
>   
>
> Fax 604-888-4732
>
>   
>
> Cel 604-790-0938
>
>   
>
> Email    [email protected]
>
>   
>
> Web www.phaserfire.ca
>
>   
>
>   
>
>   
>  _______________________________________________ Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   
  
  
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to