That seems small for a 'warehouse.' Is this within another building as a 
control area or a separate detached building? What is the occupancy class?

If this is an IBC/IFC area, be certain to review Chapter 50 and Chapter 57 of 
the IFC. There are other requirements with regards to maximum storage heights 
whether it's solid pile or on rack storage, need for secondary containment 
including fire flow, sprinkler demand, minimum distances between piles or rack, 
etc. that will apply.

I have seen/heard of very similar scenarios as described for distillery type 
facilities that are growing. I'm also confused/concerned about why the 
warehouse did not require sprinkler protection but is required by the AHJ. Our 
role is to verify code compliance, not mandate code. So if it wasn't required, 
there must be some additional things going on; is there some type of alternate 
methods and materials situation? If the AHJ is requiring sprinklers if the code 
doesn't necessitate them, I would be posing the design questions back to the 
AHJ.


[CityofLO_Seal_OptSiz#E2D662 (3)]David Smith | Deputy Fire Marshal
P 503.635.0378 | F 503.635.0376
[email protected]<mailto:[email protected]>
300 B Avenue | PO BOX 369 Lake Oswego OR 97034

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Crawford
Sent: Tuesday, May 23, 2017 4:04 PM
To: [email protected]
Subject: Flammable & Combustible storage

NFPA #30  (2008 ed)

We have a client that has a Liquid warehouse (1,200 ft²) that did not require 
sprinkler protection by code, but did require sprinkler protection by the AHJ 
to get a building permit. The system is an Ordinary hazard group 2 dry system.

They store class II and IIIB liquids in steel drums and Plastic IBC, originally 
storage was on the floor to 4'-0" one drum or tote high.

But as with all thing the company grows and they want to store higher.

Table 12.6.2.2 Quantity Limitations for unprotected Liquid Warehouses will 
allow 10'-0" of class II and 15'-0" of class IIIB

So my understanding is that unprotected is defined as not protected to NFPA 
#30, so based on Table 12.6.2.2 they can store these products to the heights 
noted even thou the area is sprinkled to NFPA #13 Ordinary hazard group 2.

Am I missing something?


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  [email protected]<mailto:[email protected]>
Web www.phaserfire.ca<http://www.phaserfire.ca>

PUBLIC RECORDS LAW DISCLOSURE This e-mail is a public record of the City of 
Lake Oswego and is subject to public disclosure unless exempt from disclosure 
under Oregon Public Records Law. This email is subject to the State Retention 
Schedule.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to