A peeve of mine.  Pads are a building code item taken out of chapter 9 and #20 
because many manufacturers are different.

Rule of thumb.  Pad is required, grouting dependent upon manufacturers base 
design.  Pad (and grout) should assume 3x the mass (weight) of driving 
equipment and extend a minimum of 6” beyond doweled anchors on all sides.

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: Monday, June 12, 2017 5:04 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: dmarti...@total-mechanical.com
Subject: RE: Pump pads

 

I was taught it was a requirement of the pump manufactures for horizontal split 
case pumps. 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org 
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> ] On Behalf Of John 
Irwin
Sent: Monday, June 12, 2017 11:11 AM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: Pump pads

 

We have a client who wants us to install our pumps directly to the floor with 
no maintenance pads. We can't find a requirement in 20 that says we must have 
pads.

 

What say you?

 

 

 

John Irwin 

Division Manager - Fire Sprinklers

Critical System Solutions 

jir...@criticalsystemsolutions.com <mailto:jir...@criticalsystemsolutions.com>  