Playing DA, (Not district Attorney), If taken out of the mandating books, how 
do we make the “other guy” do what we know is correct.

R/
Matt

Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:[email protected]]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tom Duross
Sent: Monday, June 12, 2017 6:06 PM
To: [email protected]
Subject: RE: Pump pads

A peeve of mine.  Pads are a building code item taken out of chapter 9 and #20 
because many manufacturers are different.
Rule of thumb.  Pad is required, grouting dependent upon manufacturers base 
design.  Pad (and grout) should assume 3x the mass (weight) of driving 
equipment and extend a minimum of 6” beyond doweled anchors on all sides.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Monday, June 12, 2017 5:04 PM
To: 
[email protected]<mailto:[email protected]>
Cc: [email protected]<mailto:[email protected]>
Subject: RE: Pump pads

I was taught it was a requirement of the pump manufactures for horizontal split 
case pumps.

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of John Irwin
Sent: Monday, June 12, 2017 11:11 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Pump pads

We have a client who wants us to install our pumps directly to the floor with 
no maintenance pads. We can't find a requirement in 20 that says we must have 
pads.

What say you?



John Irwin
Division Manager - Fire Sprinklers
Critical System Solutions
[email protected]<mailto:[email protected]>
813-618-2781


Sent from a mobile device. Please forgive brevity, spelling errors and 
punctuation gaffes.