Xylem Information on Pads:

Pads

Pumps are usually not anchored directly to floors, whether the floor is the 
slab-on-grade concrete floor, or an above-grade floor or the building roof. If 
installing a pump on the slab, housekeeping pads are used to elevate the pump 
and faciliate anchoring bolts. When mounted above the slab, or, when extra 
vibration control is needed, pumps are mounted on inertia bases.

Concrete pads, also called housekeeping pads, are typically 4-in. high, but the 
height depends on the size of the anchor bolts. Housekeeping pads provide a 
solid anchor, protect the pump and motor from shallow floods and floor 
cleaners, and help keep feet away from moving machinery. Housekeeping pads 
usually extend past the pump 6-in. on all sides, which provides room for 
service.

Inertia bases are used when floor-mounted pumps are on floors above grade – 
such as rooftops and mid-floor equipment rooms. They may also be used in 
noise/vibration-sensitive environments, such as performing arts centers and 
research laboratories. Inertia bases consist of heavy-duty metal frames and 
vibration isolators, and they form a cavity that is filled with concrete or 
non-shrinking grout for additional stability.  Because they cost more than 
concrete pads, engineers should only specify them when they’re really needed.


Tom Wellen


> On Jun 13, 2017, at 8:43 AM, Matt Grise <[email protected]> wrote:
> 
> Are there any documents available from the pump suppliers that show pad 
> requirements?
>  
> Matt 
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Matthew J Willis
> Sent: Tuesday, June 13, 2017 8:41 AM
> To: [email protected]
> Subject: RE: Pump pads
>  
> Playing DA, (Not district Attorney), If taken out of the mandating books, how 
> do we make the “other guy” do what we know is correct.
>  
> R/
> Matt
>  
> Matthew J. Willis
> Project Manager
> Rapid Fire Protection Inc. <http://rapidfireinc.com/>
> 1530 Samco Road
> Rapid City, SD 57702
> Office-605.348.2342
> Direct Line-605.593.5063
> Cell-605.391.2733
> Fax:-605.348.0108
>  
> <image001.png>
>  
> From: Sprinklerforum [mailto:[email protected] 
> <mailto:[email protected]>] On Behalf Of Tom 
> Duross
> Sent: Monday, June 12, 2017 6:06 PM
> To: [email protected] 
> <mailto:[email protected]>
> Subject: RE: Pump pads
>  
> A peeve of mine.  Pads are a building code item taken out of chapter 9 and 
> #20 because many manufacturers are different.
> Rule of thumb.  Pad is required, grouting dependent upon manufacturers base 
> design.  Pad (and grout) should assume 3x the mass (weight) of driving 
> equipment and extend a minimum of 6” beyond doweled anchors on all sides.
>  
> From: Sprinklerforum [mailto:[email protected] 
> <mailto:[email protected]>] On Behalf Of Dewayne 
> Martinez
> Sent: Monday, June 12, 2017 5:04 PM
> To: [email protected] 
> <mailto:[email protected]>
> Cc: [email protected] <mailto:[email protected]>
> Subject: RE: Pump pads
>  
> I was taught it was a requirement of the pump manufactures for horizontal 
> split case pumps. 
>  
> From: Sprinklerforum [mailto:[email protected] 
> <mailto:[email protected]>] On Behalf Of John 
> Irwin
> Sent: Monday, June 12, 2017 11:11 AM
> To: [email protected] 
> <mailto:[email protected]>
> Subject: Pump pads
>  
> We have a client who wants us to install our pumps directly to the floor with 
> no maintenance pads. We can't find a requirement in 20 that says we must have 
> pads.
>  
> What say you?
>  
>  
>  
> John Irwin 
> Division Manager - Fire Sprinklers
> Critical System Solutions 
> [email protected] 
> <mailto:[email protected]> 
> 813-618-2781
>  
>  
> Sent from a mobile device. Please forgive brevity, spelling errors and 
> punctuation gaffes.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to