NFPA 13R does not mandate you include the hose allowance. You have to include the domestic allowance where the split occurs.
That has always been my understanding. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:[email protected]> email:[email protected] <http://www.mfpdesign.com/> http://www.mfpdesign.com <https://www.facebook.com/pages/MFP-Design-LLC/92218417692> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: <https://www.hightail.com/u/MFPDesign> https://www.hightail.com/u/MFPDesign LinkedIn: <https://www.linkedin.com/in/travismack> https://www.linkedin.com/in/travismack **PLEASE NOTE NEW ADDRESS** From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jay White Sent: Monday, August 21, 2017 9:56 AM To: [email protected] Subject: Light Hazaed areas in NFPA 13R Building If a building is designed per NFPA 13R, a sorority house. The first floor has some common areas ( study rooms, library , entry way) that are to be designed per NFPA 13. Do you still need to include the 100 hose for light hazard. Engineer is arguing you can omit the hose allowance for the light hazard areas. Has anyone run into this? Jay White Sales/Design Manager Dynamic Fire Protection 9771 Highway 25 South Starkville, MS 39759 PH: 662-312-2426 FAX: 662-324-1545