NFPA 13R does not mandate you include the hose allowance.  You have to
include the domestic allowance where the split occurs.

 

That has always been my understanding.

 

Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:[email protected]> email:[email protected]

 

 <http://www.mfpdesign.com/> http://www.mfpdesign.com

 <https://www.facebook.com/pages/MFP-Design-LLC/92218417692>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:  <https://www.hightail.com/u/MFPDesign>
https://www.hightail.com/u/MFPDesign 

LinkedIn:  <https://www.linkedin.com/in/travismack>
https://www.linkedin.com/in/travismack

 

**PLEASE NOTE NEW ADDRESS**

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jay White
Sent: Monday, August 21, 2017 9:56 AM
To: [email protected]
Subject: Light Hazaed areas in NFPA 13R Building

 

If a building is designed per NFPA 13R, a sorority house. The first  floor
has some common areas ( study rooms, library , entry way) that are to be
designed per NFPA 13. Do you still need to include the 100 hose for light
hazard. Engineer is arguing you can omit the hose allowance for the light
hazard areas. Has anyone run into this?

 