Todd already said look at the annex bit allow me to elaborate and say the Annex explicitly says you do not include the hose demand (or protect concealed combustible spaces). IT was added to break the habit of saying design outside the dwelling unit PER NFPA 13. For outside the dwelling unit, a few specific design components from 13 are applied (aka density, area of coverage, and size of remote area).
Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> Fire Sprinklers Saves Lives > On Aug 21, 2017, at 9:56 AM, Jay White <[email protected]> wrote: > > If a building is designed per NFPA 13R, a sorority house. The first floor > has some common areas ( study rooms, library , entry way) that are to be > designed per NFPA 13. Do you still need to include the 100 hose for light > hazard. Engineer is arguing you can omit the hose allowance for the light > hazard areas. Has anyone run into this? > > Jay White > Sales/Design Manager > Dynamic Fire Protection > 9771 Highway 25 South > Starkville, MS 39759 > PH: 662-312-2426 > FAX: 662-324-1545 > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > <mailto:[email protected]> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>