Does the domestic allowance have to be included for a dedicated fire line. 
There is no domestic being supplied from this fire line.

 

Jay White

Sales/Design Manager

Dynamic Fire Protection

9771 Highway 25 South

Starkville, MS 39759

PH:   662-312-2426

FAX: 662-324-1545

 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark Sornsin [FAR]
Sent: Monday, August 21, 2017 12:01 PM
To: '[email protected]'
Subject: RE: Light Hazaed areas in NFPA 13R Building

 

Further to Travis’ answer… So just because you follow NFPA 13 densities in 
those common areas, that doesn’t mean you need to add in the hose allowances. 

(Unless the engineer specifically called them out in the contract documents – 
assuming you bid to some sort of plans/specs).

 

 


 <http://www.SummitCoUS.com> Visit our Website at www.SummitCoUS.com

Mark Sornsin  
Sr. Fire Protection Engineer
Direct: 701-499-1391
Cell: 701-526-8585

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack; MFP Design, LLC
Sent: Monday, August 21, 2017 11:58 AM
To: [email protected]
Subject: RE: Light Hazaed areas in NFPA 13R Building

 

NFPA 13R does not mandate you include the hose allowance.  You have to include 
the domestic allowance where the split occurs.

 

That has always been my understanding.

 

Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:[email protected]> email:[email protected]

 

 <http://www.mfpdesign.com/> http://www.mfpdesign.com

 <https://www.facebook.com/pages/MFP-Design-LLC/92218417692> 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:  <https://www.hightail.com/u/MFPDesign> 
https://www.hightail.com/u/MFPDesign 

LinkedIn:  <https://www.linkedin.com/in/travismack> 
https://www.linkedin.com/in/travismack

 

**PLEASE NOTE NEW ADDRESS**

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jay White
Sent: Monday, August 21, 2017 9:56 AM
To: [email protected]
Subject: Light Hazaed areas in NFPA 13R Building

 

If a building is designed per NFPA 13R, a sorority house. The first  floor has 
some common areas ( study rooms, library , entry way) that are to be designed 
per NFPA 13. Do you still need to include the 100 hose for light hazard. 
Engineer is arguing you can omit the hose allowance for the light hazard areas. 
Has anyone run into this?

 

Jay White

Sales/Design Manager

Dynamic Fire Protection

9771 Highway 25 South

Starkville, MS 39759

PH:   662-312-2426

FAX: 662-324-1545

 

 

 


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to