I felt the same way but the codes indicates differently.  It
is specifically limited to apartment buildings and in all 3 codes.  It takes
a little work to get through IBC.  NFPA 1(2015)13.3.2.17.7 & 101: 30.3.5.7
exempts sprinklers.  The key is the approved separation between occupancies.
We use IBC & NFPA with the NFPA Codes taking precedence. 

                Just a consideration.

                Dick

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Pete Schwab
Sent: Tuesday, August 29, 2017 9:54 AM
To: [email protected]
Subject: RE: Parking under 13R system

 

Dick

I have to disagree with you. If there is a residential occupancy in a
building, a sprinkler system shall be provided throughout the building.

Pete

 

 

903.2.8 Group R. An automatic sprinkler system

installed in accordance with Section 903.3 shall be provided

throughout all buildings with a Group R fire area.

 

Peter Schwab

VP of Purchasing and Engineering technologies

 

Wayne Automatic Fire Sprinklers Inc.

222 Capitol Court

Ocoee, Fl 34761

 

Mobile: (407) 468-8248

Direct: (407) 877-5570

Fax: (407) 656-8026

 

www.waynefire.com <http://www.waynefire.com/> 

 



 

I sleep in a sprinklered home, do you? 

 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Dick Culver
Sent: Tuesday, August 29, 2017 9:44 AM
To: [email protected]
<mailto:[email protected]> 
Subject: RE: Parking under 13R system

 

I have not seen this put out there.  Does the parking area meet the
definition of an "open" parking structure in accordance with NFPA 88A, if so
NFPA 101, NFPA 1 and IBC do not require protection under apartment
buildings.  The architect has to maintain the proper horizontal separation.


 

                Dick

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Monday, August 28, 2017 6:55 PM
To: [email protected]
<mailto:[email protected]> 
Subject: Re: Parking under 13R system

 

For whatever it's worth, we anticipated this in California and made
amendments to NFPA 13D and also the building code that address open carports
with living space above. Obviously, the requirement is to furnish
sprinklers.

 

 

Steve

 

 

-------- Original message --------

From: Rocci Cetani 3 <[email protected] <mailto:[email protected]> >


Date: 8/28/17 4:35 PM (GMT-05:00) 

To: [email protected]
<mailto:[email protected]>  

Subject: RE: Parking under 13R system 

 

The problem is there is no definition for carport so it leave it open to
personal interpretation.. I did a quick search and most of the  definitions
I can find  say this or something similar  "a shelter for a car consisting
of a roof supported on posts, built beside a house".  I always think of
carports as covered parking usually in front of the building. I wouldn't
feel comfortable omitting sprinklers from a parking area below an occupied
multi-tenant space. 

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

[email protected] <mailto:[email protected]> 

www.norcalfire.com <http://www.norcalfire.com/> 

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected] <mailto:[email protected]> 
Sent: Monday, August 28, 2017 1:14 PM
To: Sprinklerforum
Subject: Re: Parking under 13R system

 

Rocco,

 

But could it fall under the definition of a carport and be excluded per
6.6.5?


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 <tel:860-535-2080>  (ofc)

860-553-3553 <tel:860-553-3553>  (fax)

860-608-4559 <tel:860-608-4559>  (cell)

 

On Aug 28, 2017 at 9:25 AM, <Rocci Cetani 3 <mailto:[email protected]> >
wrote:

Since its doesn't fall under the definition of garages per 7.3.2 you are
directed to 7.2. We had this situation a few months ago on a project and
protected it per NFPA 13 OH 1 for parking garages.

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

[email protected] <mailto:[email protected]> 

www.norcalfire.com <http://www.norcalfire.com/> 

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected] <mailto:[email protected]> 
Sent: Friday, August 25, 2017 3:30 AM
To: Sprinklerforum
Subject: Parking under 13R system

 

I am looking at a 3 story apartment building that is going to be protected
by a 13R system. Under one wing, the main level will be open for parking
with 2 floors of apartments above. 13R addresses garages but not open (on 2
sides) parking areas. A number of years ago, I did a similar arrangement,
but it was a 13 system and the space was protected by a dry system. Thought
on if sprinklers are required?

 

I know there was a thread or 2 about this, but only found the one about
sprinklers under train tracks. 


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 <tel:860-535-2080>  (ofc)

860-553-3553 <tel:860-553-3553>  (fax)

860-608-4559 <tel:860-608-4559>  (cell)

_______________________________________________ Sprinklerforum mailing list
[email protected]
<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to