IFC 905.4 states that hose connections shall be provided on each side of the wall adjacent to horizontal exits, except where there is an exit stairway located within 130 feet (100' of hose + 30' of stream).
In order to omit hose connections from both sides of the horizontal exit, am I required to have two exit stairs (one in each fire area) located within 130 feet of the horizontal exit, reachable from both sides? Or is any one exit stairway within 130 feet of the horizontal exit OK? Kyle Montgomery [cid:[email protected]] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell: 602.763.4736 [email protected]<mailto:[email protected]>