1.  Why are they asking for 7 heads in a 300 sq. ft. room?  Does this include 
sub-level heads below obstructions?
  2.  Are you providing high expansion foam, only HEF will “fill a room”.
  3.  Foam-water systems are typically provided to protect areas subject to 
pool fires.  The idea is to create a foam blanket at the floor level over the 
spill.
  4.  Foam-water systems are typically either 94% or 97% water with regards to 
what comes out of the sprinklers.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, September 26, 2017 8:27 AM
To: Sprinkler Forum <[email protected]>
Subject: Life Safety in Foam Systems [EXTERNAL]

Since I couldn't find the Foam Forum, I figured I would ask this here. I have 
been asked to design a modification to an existing foam system inside a 
building. I am still trying to get details on occupancy, design, etc. There is 
no one in the room on a regular basis, but there is occasionally. My concern 
(at this point) is that they are asking for 7 sprinklers (closed) in a 300 sqft 
room. Are there any life safety concerns with this? I wouldn't want to see 
someone get trapped in a room filling up with foam.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-553-3553<tel:860-553-3553> (fax)
860-608-4559<tel:860-608-4559> (cell)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to