This section of the IFC is, let’s say, horribly written.  905.3.1 starts off 
say ALL shall be Class III then provides an exception whereby Class I is 
allowed when the building s fully sprinklered.  Then 905.3.2 specifically calls 
for a Class I for large Assembly occupancies (occupant load over 1,000).  NFPA 
14 is much cleaner but let’s let the Chair of that TC comment on correlation 
with the IFC.

Ball teed-up.  Whack it Steve.

Roland

Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Nov 1, 2017, at 12:27 PM, Thomas Reinhardt <[email protected]> 
> wrote:
> 
> The highest story is above 30 feet. Thus are adopted IFC chapter 9 section 
> 905.3.1 apply. Standpipes to be automatic wet. Thanks