That wasn't an opinion about the standard, it was a neutral narrative to 
underscore what Huggins said about the code.  And I'll express my opinions when 
I want to.  For example ... you're a bozo.

Sorry Roland and Frank, I'm off topic.

SML

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Sprinkler Academy - C Bilbo
Sent: Wednesday, November 01, 2017 1:01 PM
To: [email protected]
Subject: Re: Standpipe Pressure Question.


Hey, hey, hey...... let's all hold on here.



It's my understanding that the chair of an NFPA Committee "is not supposed to 
have an opinion".



Now, with that said...... whatever Steve says about standpipes is gold. (Please 
don't kick me off the committee Mr. Chair.)




It should be recognized that the above is my opinion as a member of the NFPA, 
and has not been processed as a formal interpretation in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the the NFPA, nor any 
of their technical committees.

Sincerely,


Cecil Bilbo
Director of Training and Education
Fire Protection Group
Shambaugh & Son, LP
Champaign, IL
[email protected]<mailto:[email protected]>



________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, November 1, 2017 2:50 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Standpipe Pressure Question.


To what Roland says, 905.3.1 does not require automatic standpipes in a 
building, only that standpipes are required based on absolute height or 
buildings four stories and higher.   The special requirements for high-rise 
buildings are in other sections of the building code and in NFPA 14.



SML



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Wednesday, November 01, 2017 12:46 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Standpipe Pressure Question.



This section of the IFC is, let's say, horribly written.  905.3.1 starts off 
say ALL shall be Class III then provides an exception whereby Class I is 
allowed when the building s fully sprinklered.  Then 905.3.2 specifically calls 
for a Class I for large Assembly occupancies (occupant load over 1,000).  NFPA 
14 is much cleaner but let's let the Chair of that TC comment on correlation 
with the IFC.



Ball teed-up.  Whack it Steve.



Roland



Roland Huggins, PE - Senior VP Engineering

American Fire Sprinkler Assn.

Dallas, TX

http://www.firesprinkler.org<https://nam02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.firesprinkler.org%2F&data=02%7C01%7Cprodesigngroup%40msn.com%7C205fb74265cb41b0ac1908d52161c0f7%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636451626085903034&sdata=lc1rzPCqCe%2FnLOJucUldFjscyEJ59UXnj7cn%2BSwWYz8%3D&reserved=0>



Fire Sprinklers Saves Lives







On Nov 1, 2017, at 12:27 PM, Thomas Reinhardt 
<[email protected]<mailto:[email protected]>> wrote:



The highest story is above 30 feet. Thus are adopted IFC chapter 9 section 
905.3.1 apply. Standpipes to be automatic wet. Thanks


_______________________________________________