To what Roland says, 905.3.1 does not require automatic standpipes in a 
building, only that standpipes are required based on absolute height or 
buildings four stories and higher.   The special requirements for high-rise 
buildings are in other sections of the building code and in NFPA 14.

SML

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Wednesday, November 01, 2017 12:46 PM
To: [email protected]
Subject: Re: Standpipe Pressure Question.

This section of the IFC is, let’s say, horribly written.  905.3.1 starts off 
say ALL shall be Class III then provides an exception whereby Class I is 
allowed when the building s fully sprinklered.  Then 905.3.2 specifically calls 
for a Class I for large Assembly occupancies (occupant load over 1,000).  NFPA 
14 is much cleaner but let’s let the Chair of that TC comment on correlation 
with the IFC.

Ball teed-up.  Whack it Steve.

Roland

Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.
Dallas, TX
http://www.firesprinkler.org<http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives



On Nov 1, 2017, at 12:27 PM, Thomas Reinhardt 
<[email protected]<mailto:[email protected]>> wrote:

The highest story is above 30 feet. Thus are adopted IFC chapter 9 section 
905.3.1 apply. Standpipes to be automatic wet. Thanks