Nope. HSW is not an option.


John Irwin

DynaFire Inc.



*From:* Sprinklerforum [mailto:
sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Matt Grise
*Sent:* Tuesday, November 21, 2017 7:33 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* RE: [EXTERNAL] Interesting issue .. residential sprinklers ..



Any soffits over bathrooms or HVAC supply? We have done 20x20 sidewalls in
places like this.



Matt



*From:* Sprinklerforum [
mailto:sprinklerforum-boun...@lists.firesprinkler.org
<sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Ed.Tambini
*Sent:* Tuesday, November 21, 2017 6:20 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* RE: [EXTERNAL] Interesting issue .. residential sprinklers ..



Use half of a riser clamp and put the pipe tight to the deck





*From:* Sprinklerforum [
mailto:sprinklerforum-boun...@lists.firesprinkler.org
<sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *John Irwin
*Sent:* Tuesday, November 21, 2017 4:27 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* [EXTERNAL] Interesting issue .. residential sprinklers ..



I am working on a project with a lot of 20x20 rooms in dwelling units. I
have a concrete deck so my piping will be exposed. I am trying to find a
20x20 solutions but keep running in to road blocks. Maybe someone has an
idea.



The way I see it, I need one of the following …



I need a residential pendent sprinkler that can be installed with a
deflector distance from the deck greater than allowed by NFPA 13 OR I need
a residential UPRIGHT sprinkler listed for 20x20 spacing OR I need a listed
hanger attachment that will allow me to install 1" branch piping tight to a
concrete deck.



And go.