Residential sprinklers are “permitted” in dwelling units, not “required”, 
right? Couldn’t you use any one of a number of commercial QR extended coverage 
sprinklers?

That might mess you up if you are trying to do a 4-sprinklers residential calc… 
or it could help because you could get a larger K-factor and lower starting 
pressure for 20x20.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Irwin
Sent: Tuesday, November 21, 2017 4:27 AM
To: [email protected]
Subject: [EXTERNAL] Interesting issue .. residential sprinklers ..

I am working on a project with a lot of 20x20 rooms in dwelling units. I have a 
concrete deck so my piping will be exposed. I am trying to find a 20x20 
solutions but keep running in to road blocks. Maybe someone has an idea.

The way I see it, I need one of the following …


I need a residential pendent sprinkler that can be installed with a deflector 
distance from the deck greater than allowed by NFPA 13 OR I need a residential 
UPRIGHT sprinkler listed for 20x20 spacing OR I need a listed hanger attachment 
that will allow me to install 1" branch piping tight to a concrete deck.



And go.


John Irwin
DynaFire, Inc.