Well this Arch decided to put the skylights closer than 10’-0”

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Pete Schwab
Sent: Friday, January 05, 2018 12:44 PM
To: [email protected]
Subject: RE: Deflector Distance for Sprinklers in Skylights

 

Bruce

It was corrected in the 2016 edition. 8.5 applies to all types of sprinklers.

 

 

8.5.7 Skylights.

8.5.7.1 Sprinklers shall be permitted to be omitted from skylights

not exceeding 32 ft2 (3.0 m2) in area, regardless of hazard

classification, that are separated by at least 10 ft (3.0 m)

horizontally from any other unprotected skylight or unprotected

ceiling pocket.

8.5.7.1.1 When a sprinkler is installed directly beneath a skylight

not exceeding 32 ft2 (3.0 m2), the distance to the ceiling

shall be measured to the plane of the ceiling as if the skylight

was not present.

 

Peter Schwab

VP of Purchasing and Engineering technologies

 

Wayne Automatic Fire Sprinklers Inc.

222 Capitol Court

Ocoee, Fl 34761

 

Mobile: (407) 468-8248

Direct: (407) 877-5570

Fax: (407) 656-8026

 

www.waynefire.com <http://www.waynefire.com/> 

 

cid:[email protected]

 

I sleep in a sprinklered home, do you? 

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bruce Verhei
Sent: Friday, January 5, 2018 3:32 PM
To: [email protected]
Subject: Re: Deflector Distance for Sprinklers in Skylights

 

I think the requirement for sprinkler heads in skylights is a part of the code 
that no one has corrected due to lack of interest. 

 

When put in a skylight meant a set of glass windows at the top a light well. 
The light well is feet deep as it passes through the heavy wood truss roof 
structure. Think 1920’s buildings. The wainscoting type material separating the 
light well from the attic space has no effective fire resistance.

 

The skylight or smoke vent that is mounted on top of curbing, which in turn it 
mounted on top of the roof sheathing is entirely different, as far as fire 
spread. 

 

Putting sprinklers in these skylights has no particular benefit. 

 

 

Best.

 

Bruce Verhei 


On Jan 5, 2018, at 10:09, Jerry Van Kolken <[email protected]> wrote:

I have a project that will require sprinkler in the common bubble canopy 
skylights. What do I measure my deflector down from? The top of the bubble? Top 
of the window sill for the skylight?

 

Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to