Are the skylights less than 32 square feet?

If so, does 8.5.7.1.1 apply? If so, there’s your answer…

But I’m not sure if it does since 8.5.7.1.1 is a “subtext” to 8.5.7.1, which is 
specific to situations where the skylights are less than 32 square feet AND 
separated by at least 10 feet. But 8.5.7.1.1 only refers to skylights less than 
32 square feet, and doesn’t mention separation distance.

So basically… I can be of no help to you. But I am curious what the answer is.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jerry Van Kolken
Sent: Friday, January 05, 2018 3:06 PM
To: [email protected]
Subject: [EXTERNAL] RE: Deflector Distance for Sprinklers in Skylights

Well this Arch decided to put the skylights closer than 10’-0”

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Pete Schwab
Sent: Friday, January 05, 2018 12:44 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Deflector Distance for Sprinklers in Skylights

Bruce
It was corrected in the 2016 edition. 8.5 applies to all types of sprinklers.


8.5.7 Skylights.
8.5.7.1 Sprinklers shall be permitted to be omitted from skylights
not exceeding 32 ft2 (3.0 m2) in area, regardless of hazard
classification, that are separated by at least 10 ft (3.0 m)
horizontally from any other unprotected skylight or unprotected
ceiling pocket.
8.5.7.1.1 When a sprinkler is installed directly beneath a skylight
not exceeding 32 ft2 (3.0 m2), the distance to the ceiling
shall be measured to the plane of the ceiling as if the skylight
was not present.

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

http://secure-web.cisco.com/1HLxbaIjfje8A16BDOVuyKPV32q7R2cP3LX9NV8sberfqc6maW0ET6kgwaW_Jso4ZkEZrSfJS22Hb9eWqQXeyqsXhcyFYyMTQanFFRAB9VmZvbvL9_8r0TvZkPt3Y-GdZKvuRqVcKjYbbnYK7bA_Ks3fBjy9phrLTTIDELQ2iAFA2xJwesC_HlNuYUiExnhigmdZs-1Y3CNI1bGnrU42-JiXAPwqFtVObTLgjixVmc01IgfC16Kf-qCGt7nZa25FttuUCSGqHRf4_UEwMNnxDAw/http%3A%2F%2Fwww.waynefire.com<http://secure-web.cisco.com/1WjF50HwoFZ9BrFYfLlDgDl744dbsD2Unny-yPXGYyM0L7TbPJDI1SA3ArrimWnB43cN1LMHI9VYOo1sIlaTRm6DRwy3gmztFD9tNHYbWmj4BMAKaBhknldA1wx6FTSG01oxPnnT9PviI0r6aLzy6WIadl016Hsb8DE7Hrn26Dd_e3ZZO35YIMPXPwirj5Yqr4d4jCrDfVSj8aNa22s5hx5wsai0rqakwEtl-Dc30uGr8XK8lWRGBjYR_13h0Z686-SWVBXROWdDRs1BinDdO0w/http%3A%2F%2Fwww.waynefire.com%2F>

[cid:[email protected]]

I sleep in a sprinklered home, do you?


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bruce Verhei
Sent: Friday, January 5, 2018 3:32 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Deflector Distance for Sprinklers in Skylights

I think the requirement for sprinkler heads in skylights is a part of the code 
that no one has corrected due to lack of interest.

When put in a skylight meant a set of glass windows at the top a light well. 
The light well is feet deep as it passes through the heavy wood truss roof 
structure. Think 1920’s buildings. The wainscoting type material separating the 
light well from the attic space has no effective fire resistance.

The skylight or smoke vent that is mounted on top of curbing, which in turn it 
mounted on top of the roof sheathing is entirely different, as far as fire 
spread.

Putting sprinklers in these skylights has no particular benefit.


Best.

Bruce Verhei

On Jan 5, 2018, at 10:09, Jerry Van Kolken 
<[email protected]<mailto:[email protected]>> wrote:
I have a project that will require sprinkler in the common bubble canopy 
skylights. What do I measure my deflector down from? The top of the bubble? Top 
of the window sill for the skylight?

Jerry Van Kolken
Millennium Fire Protection Corp.
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://secure-web.cisco.com/1aE0WSCattYua2ypESEKQXL4QHUviuZwc0iipjziiUJKya9DO8srTlAXeDMdDrw3Sk2rDdr_xIvuelDe2b5qP7Y9Bnz-UQ-PYt8x6gJ0CIUE9Hh_hXgpgm_JvufEIZfVeLzYEKcubaCmDOkVidRttTlQVFzKU5wLxd7oKI0oF8oEf_MO0QhGoUSwEb612VZnwOV3HsjONdGkGwfraYVcJH7XfHSjXETSOmid8rwJ3SHhZwJydAWf2D45g8p9EbsKPt1hguYrbtJMMf0IQ2I6M5w/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to