One big difference on skylights (vs ceiling pockets) is that the depth is irrelevant.
Interesting point about ignoring difference if the combined area is NMT 32 sf. Remember that we once add the same 10 ft requirements for ceiling pockets and it evolved to looking at it as a grouping and the related volumetric total. Since skylights have no volume limits, that tells us that it’s all about the opening NOT capturing the fire plume. It’s a fuzzy issue since two skylights (16 sf each) that are side by side will have a different impact on the ceiling jet than a single 32 sf opening. How much so, we’ll have to play with it and see (not exactly a front burner issue but an interesting academic item for this family of sprinkler nerds). Roland Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> Fire Sprinklers Saves Lives > On Jan 5, 2018, at 2:53 PM, Jerry Van Kolken <[email protected]> wrote: > > The bottom of the opening exceeds 32 sqft then they taper into a 18sqft > skylight, but the depth also exceeds 36” as well. > > Jerry Van Kolken > Millennium Fire Protection > (760) 722-2722 > > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Kyle.Montgomery > Sent: Friday, January 05, 2018 2:35 PM > To: [email protected] > Subject: RE: [EXTERNAL] RE: Deflector Distance for Sprinklers in Skylights > > Are the skylights less than 32 square feet? > > If so, does 8.5.7.1.1 apply? If so, there’s your answer… > > But I’m not sure if it does since 8.5.7.1.1 is a “subtext” to 8.5.7.1, which > is specific to situations where the skylights are less than 32 square feet > AND separated by at least 10 feet. But 8.5.7.1.1 only refers to skylights > less than 32 square feet, and doesn’t mention separation distance. > > So basically… I can be of no help to you. But I am curious what the answer is. > > -Kyle M > > From: Sprinklerforum [mailto:[email protected] > <mailto:[email protected]>] On Behalf Of Jerry > Van Kolken > Sent: Friday, January 05, 2018 3:06 PM > To: [email protected] > <mailto:[email protected]> > Subject: [EXTERNAL] RE: Deflector Distance for Sprinklers in Skylights > > Well this Arch decided to put the skylights closer than 10’-0” > > Jerry Van Kolken > Millennium Fire Protection > (760) 722-2722 > > From: Sprinklerforum [mailto:[email protected] > <mailto:[email protected]>] On Behalf Of Pete > Schwab > Sent: Friday, January 05, 2018 12:44 PM > To: [email protected] > <mailto:[email protected]> > Subject: RE: Deflector Distance for Sprinklers in Skylights > > Bruce > It was corrected in the 2016 edition. 8.5 applies to all types of sprinklers. > > > 8.5.7 Skylights. > 8.5.7.1 Sprinklers shall be permitted to be omitted from skylights > not exceeding 32 ft2 (3.0 m2) in area, regardless of hazard > classification, that are separated by at least 10 ft (3.0 m) > horizontally from any other unprotected skylight or unprotected > ceiling pocket. > 8.5.7.1.1 When a sprinkler is installed directly beneath a skylight > not exceeding 32 ft2 (3.0 m2), the distance to the ceiling > shall be measured to the plane of the ceiling as if the skylight > was not present. > > Peter Schwab > VP of Purchasing and Engineering technologies > > Wayne Automatic Fire Sprinklers Inc. > 222 Capitol Court > Ocoee, Fl 34761 > > Mobile: (407) 468-8248 > Direct: (407) 877-5570 > Fax: (407) 656-8026 > > http://secure-web.cisco.com/1HLxbaIjfje8A16BDOVuyKPV32q7R2cP3LX9NV8sberfqc6maW0ET6kgwaW_Jso4ZkEZrSfJS22Hb9eWqQXeyqsXhcyFYyMTQanFFRAB9VmZvbvL9_8r0TvZkPt3Y-GdZKvuRqVcKjYbbnYK7bA_Ks3fBjy9phrLTTIDELQ2iAFA2xJwesC_HlNuYUiExnhigmdZs-1Y3CNI1bGnrU42-JiXAPwqFtVObTLgjixVmc01IgfC16Kf-qCGt7nZa25FttuUCSGqHRf4_UEwMNnxDAw/http%3A%2F%2Fwww.waynefire.com > > <http://secure-web.cisco.com/1WjF50HwoFZ9BrFYfLlDgDl744dbsD2Unny-yPXGYyM0L7TbPJDI1SA3ArrimWnB43cN1LMHI9VYOo1sIlaTRm6DRwy3gmztFD9tNHYbWmj4BMAKaBhknldA1wx6FTSG01oxPnnT9PviI0r6aLzy6WIadl016Hsb8DE7Hrn26Dd_e3ZZO35YIMPXPwirj5Yqr4d4jCrDfVSj8aNa22s5hx5wsai0rqakwEtl-Dc30uGr8XK8lWRGBjYR_13h0Z686-SWVBXROWdDRs1BinDdO0w/http%3A%2F%2Fwww.waynefire.com%2F> > > <image001.jpg> > > I sleep in a sprinklered home, do you? > > > From: Sprinklerforum [mailto:[email protected] > <mailto:[email protected]>] On Behalf Of Bruce > Verhei > Sent: Friday, January 5, 2018 3:32 PM > To: [email protected] > <mailto:[email protected]> > Subject: Re: Deflector Distance for Sprinklers in Skylights > > I think the requirement for sprinkler heads in skylights is a part of the > code that no one has corrected due to lack of interest. > > When put in a skylight meant a set of glass windows at the top a light well. > The light well is feet deep as it passes through the heavy wood truss roof > structure. Think 1920’s buildings. The wainscoting type material separating > the light well from the attic space has no effective fire resistance. > > The skylight or smoke vent that is mounted on top of curbing, which in turn > it mounted on top of the roof sheathing is entirely different, as far as fire > spread. > > Putting sprinklers in these skylights has no particular benefit. > > > Best. > > Bruce Verhei > > On Jan 5, 2018, at 10:09, Jerry Van Kolken <[email protected] > <mailto:[email protected]>> wrote: > >> I have a project that will require sprinkler in the common bubble canopy >> skylights. What do I measure my deflector down from? The top of the bubble? >> Top of the window sill for the skylight? >> >> Jerry Van Kolken >> Millennium Fire Protection Corp. >> 2950 San Luis Rey Rd. >> Oceanside, CA 92058 >> (760) 722-2722 FX 722-2730 >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> <mailto:[email protected]> >> http://secure-web.cisco.com/1aE0WSCattYua2ypESEKQXL4QHUviuZwc0iipjziiUJKya9DO8srTlAXeDMdDrw3Sk2rDdr_xIvuelDe2b5qP7Y9Bnz-UQ-PYt8x6gJ0CIUE9Hh_hXgpgm_JvufEIZfVeLzYEKcubaCmDOkVidRttTlQVFzKU5wLxd7oKI0oF8oEf_MO0QhGoUSwEb612VZnwOV3HsjONdGkGwfraYVcJH7XfHSjXETSOmid8rwJ3SHhZwJydAWf2D45g8p9EbsKPt1hguYrbtJMMf0IQ2I6M5w/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org >> >> <http://secure-web.cisco.com/1aE0WSCattYua2ypESEKQXL4QHUviuZwc0iipjziiUJKya9DO8srTlAXeDMdDrw3Sk2rDdr_xIvuelDe2b5qP7Y9Bnz-UQ-PYt8x6gJ0CIUE9Hh_hXgpgm_JvufEIZfVeLzYEKcubaCmDOkVidRttTlQVFzKU5wLxd7oKI0oF8oEf_MO0QhGoUSwEb612VZnwOV3HsjONdGkGwfraYVcJH7XfHSjXETSOmid8rwJ3SHhZwJydAWf2D45g8p9EbsKPt1hguYrbtJMMf0IQ2I6M5w/http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org>_______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org