Xanax.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Crawford
Sent: Thursday, January 25, 2018 9:56 AM
To: [email protected]
Subject: Rubber Tire Storage

NFPA #13 (2013) is my reference.

I have an AHJ that is telling me that Rubber Tires are classified as a Group 
"A" plastic for the purpose of commodity classifications.

I have informed him that Rubber Tires are a commodity classification on their 
own, but he disagrees, he says there are a synthetic rubber so are a Group "A" 
plastic.

I have shown him the Table A5.6.3 for Commodity classifications in NFPA #13 
where rubber tires are not mentioned and chapter 18 that deals with Rubber Tire 
storage but he still disagrees.

Any suggestions?


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  [email protected]<mailto:[email protected]>
Web www.phaserfire.ca<http://www.phaserfire.ca>