Working on my best practices for Seismic projects.  Does NFPA 13 9.3.5.9.7 
("Concrete Concrete anchors shall be prequalified for seismic applications in 
accordance with ACI 355.2, Qualification of Post-Installed Mechanical Anchors 
in Concrete and Commentary, and installed in accordance with the manufacturer's 
instructions.") apply to anchors for standard supports for the system piping or 
does it only apply to sway brace components?  Section 9.3.5 applies to Sway 
Brace Design, so my gut is to say it does not.  I can find nothing in section 
9.1 or 9.2 that specifies prequalified anchors are required for standard 
supports, but logic tells me that should be a consideration as well.  What is 
the opinion(s) of the forum?  Should I be trying to convince my clients to use 
ICC evaluated anchors for all hangers?

Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV

Dynamic Fire Designs



Mail: [email protected]
Mobile: 931-242-1299
www.dynamicfiredesigns.com<http://dynamicfiredesigns.com>

Dynamic Fire Designs * 13063 Count Line Rd. Box #87 * Spring Hill * FL * 34609

This message is confidential. It may also be privileged or otherwise protected 
by work product immunity or other legal rules. If you have received it by 
mistake, please let us know by e-mail reply and delete it from your system; you 
may not copy this message or disclose its contents to anyone. The integrity and 
security of this message cannot be guaranteed on the Internet.



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to