You can only have a maximum of 4 QR sprinklers per dwelling unit, not just
compartment.  If you need more than 4 standard spray sprinklers, you can't
comply with 13R.


Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign 
LinkedIn: https://www.linkedin.com/in/travismack

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Art Tiroly
Sent: Monday, March 5, 2018 4:00 PM
To: [email protected]
Subject: RE: Residential Sprinklers

Using 5.6K QR heads will change the hydraulic calculations and minimum flows
allowed by residential sprinklers.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Reed A. Roisum, SET
Sent: Monday, March 05, 2018 4:47 PM
To: [email protected]
Subject: Residential Sprinklers

Are residential sprinklers required for dwelling units in NFPA 13R?  It
appears as though they can be QR or residential in the 2012 IBC (903.3.2).
For some reason I had in my mind that they needed to be residential within
the dwelling unit or sleeping unit??

Thanks.

Reed R.

Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 |
http://www.kfiengineers.com


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to