If this is a new building, have a chat with the structural engineer, they 
should be able to give some info regarding how much movement is expected.  I've 
worked on warehouses with high ceilings (in non-seismic zones) where the 
structural engineer would not allow us to cross the expansion joint without 
accounting for movement.

Cheers
Don

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: 2018/04/11 5:01 PM
To: [email protected]
Subject: RE: Expansion Joint

Travis-
We're on the same page. So what about expansions joints on a non-seismic job?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of MFP Design, LLC
Sent: Wednesday, April 11, 2018 5:00 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Expansion Joint

Yes.  If you are in 9.3, you are doing seismic bracing.  If you are Seismic 
Design Cat A or B, typically you are not going to do seismic and 9.3 with it's 
sub chapters would not apply.

[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]<mailto:email:[email protected]>

http://www.mfpdesign.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Brian Harris
Sent: Wednesday, April 11, 2018 1:58 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Expansion Joint

I saw that but isn't that only for systems with seismic bracing?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gus Olson
Sent: Wednesday, April 11, 2018 4:55 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Expansion Joint

9.3.2.3.1 (4)   NFPA-2013

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Wednesday, April 11, 2018 4:47 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Expansion Joint

Trying to find something in NFPA-13 that addresses expansion joints, not a 
seismic separation, but come up empty. Any help?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to