That is my exact thought on it. Now to explain that to Transportation & Works on Thursday....

On 4/24/2018 4:06 PM, Prahl, Craig/GVL wrote:

If this is just a vertical in-line drawing from a potable water source, there is no need for a strainer.It doesn’t matter if it’s an in-line or HSC, what matters is the water source.You shouldn’t have anything in a potable source that could clog up a fire pump.At least we hope not.J

Craig Prahl |Jacobs| Group Lead – Fire Protection | 864.676.5252 | [email protected]|www.jacobs.com <http://www.jacobs.com/>

*From:*Sprinklerforum [mailto:[email protected]] *On Behalf Of *P & P Sprinklers Ltd
*Sent:* Tuesday, April 24, 2018 2:33 PM
*To:* [email protected]
*Subject:* Re: [EXTERNAL] RE: Strainer ahead of fire pump

We are protecting a new school that is running off city water. The town is supplied water from a pond via their own pumps. I would assume the water is already treated. The thing is, this install has been completed since last year and only now are they getting around to commissioning and are looking for a strainer they say was required. There was no mention of a strainer on the drawings, although there was a line in the spec with reference to one.

On 4/24/2018 3:53 PM, Prahl, Craig/GVL wrote:

    If you’re drawing from any open pond or other raw water source you
    need to provide a strainer.

    Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252
    | [email protected] <mailto:[email protected]> |
    www.jacobs.com <http://www.jacobs.com/>

    *From:* Sprinklerforum
    [mailto:[email protected]] *On Behalf
    Of *Tom Duross
    *Sent:* Tuesday, April 24, 2018 2:11 PM
    *To:* [email protected]
    <mailto:[email protected]>
    *Subject:* [EXTERNAL] RE: Strainer ahead of fire pump

    Actually I think if the pump has no cleanout provisions, a
    strainer is required on vertical inline pumps.

    *From:*Sprinklerforum
    [mailto:[email protected]] *On Behalf
    Of *P & P Sprinklers Ltd
    *Sent:* Tuesday, April 24, 2018 2:08 PM
    *To:* [email protected]
    <mailto:[email protected]>
    *Subject:* Re: Strainer ahead of fire pump

    Would I be right in assuming that the wording "where necessary"
    implies that it should be avoided unless necessary?

    On 4/24/2018 3:27 PM, MFP Design, LLC wrote:

        *It’s not required but is permitted.*

        **

        MFP_logo_F

        Travis Mack, SET

        MFP Design, LLC

        3356 E Vallejo Ct

        Gilbert, AZ 85298

        480-505-9271

        fax: 866-430-6107

        email:[email protected] <mailto:email:[email protected]>

        http://www.mfpdesign.com
        
<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttp-253A-252F-252Fwww.mfpdesign.com-252F-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DHJ8OA4xyeHAoxXNz5mu-252FYfycgtd5nsFrrpvzulZiNkQ-253D-26reserved-3D0&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=tvIzK3RY_-Gey4GF4i5zgndplGh8OzDLxzAzKoRwcvM&s=xTvdPOenUtcoLD_qv-qOE5AX-OZL1N5rdLq74S1Lvpw&e=>

        https://www.facebook.com/pages/MFP-Design-LLC/92218417692
        
<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.facebook.com-252Fpages-252FMFP-2DDesign-2DLLC-252F92218417692-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DH-252BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk-253D-26reserved-3D0&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=tvIzK3RY_-Gey4GF4i5zgndplGh8OzDLxzAzKoRwcvM&s=2XjdolqpW6uLl2_s1KM92f9jXNh34kkNFoB05ovD9Qk&e=>

        Send large files to us via:
        https://www.hightail.com/u/MFPDesign
        
<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=tvIzK3RY_-Gey4GF4i5zgndplGh8OzDLxzAzKoRwcvM&s=RsrvxMaOfKfiflQNI_PauxpGansfjaRHBy_-00T1kvk&e=>

        LinkedIn: https://www.linkedin.com/in/travismack
        
<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=tvIzK3RY_-Gey4GF4i5zgndplGh8OzDLxzAzKoRwcvM&s=mVFw8ZGgaDJyM_1hKUL6JNBu00QZvueFtbsDtE4PbwQ&e=>

        */“/**/The bitterness of poor quality remains long after the
        sweetness of low price is forgotten./**/”/*

        **

        *From:*Sprinklerforum
        <[email protected]>
        <mailto:[email protected]> *On
        Behalf Of *P & P Sprinklers Ltd
        *Sent:* Tuesday, April 24, 2018 10:57 AM
        *To:* [email protected]
        <mailto:[email protected]>
        *Subject:* Strainer ahead of fire pump

        Is a strainer required before a Vertical in-line pump? All I
        can find regarding strainers in NFPA 20, 2010 ed. is the
        following:

        /4.14.9.2 The following devices shall be permitted in the
        suction piping where the following requirements are met:

            (4) Suction strainers shall be permitted to be installed
        in the
            suction piping where required by other sections of this
            standard./

        /6.3.2 Where necessary, the following fittings shall be provided:/

        /(5) Pipeline strainer/



        _______________________________________________

        Sprinklerforum mailing list

        [email protected]
        <mailto:[email protected]>

        
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
        
<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=tvIzK3RY_-Gey4GF4i5zgndplGh8OzDLxzAzKoRwcvM&s=ePScgnT1ZZ0sapsqAMqfavteZPOUee_wLKu5LYYpV-U&e=>

    
________________________________________________________________________________________

    NOTICE - This communication may contain confidential and
    privileged information that is for the sole use of the intended
    recipient. Any viewing, copying or distribution of, or reliance on
    this message by unintended recipients is strictly prohibited. If
    you have received this message in error, please notify us
    immediately by replying to the message and deleting it from your
    computer.




    _______________________________________________

    Sprinklerforum mailing list

    [email protected]
    <mailto:[email protected]>

    http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
    
<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMDaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=EJ3nd2jGynUnHiIWNlSVA-OzUrPjsDLHCyEMaRXlk7g&s=Aa0Q98_MAAcNJRLS7PHJcgVDYW69VmjlRnalHnOhZRY&e=>



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to