Have you looked at
DeWalts
Mini-Undercut+ anchor is an internally threaded, self-undercutting anchor
designed for performance in cracked and uncracked concrete

On Mon, May 7, 2018 at 7:25 AM, Kyle.Montgomery <[email protected]>
wrote:

> So, what did you find, Brad? I've not had luck being able to use drop-ins
> in seismic areas. Seems like there is always a roadblock with lack of ICC
> report, or not being acknowledged in COLA (for Los Angeles), or not being
> appropriate for 'cracked concrete' scenarios. Did you find an avenue that
> allows them?
>
> -Kyle M
>
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected].
> org] On Behalf Of [email protected]
> Sent: Saturday, May 5, 2018 2:43 PM
> To: [email protected]
> Subject: [EXTERNAL] Re: Drop In Anchors for Seismic
>
> Hello again. I found was I was looking for and it appears my fears were
> unfounded -- I didn't want to go through all the calculations satisfying 13
> only to discover 'nobody makes it'.
> Like the chicken / egg question -- tc members write rules / manufacturers
> make things to satisfy rules.
> I think with sway bracing it is egg / chicken.
>
> Brad
>
> Quoting [email protected]:
>
> > Hello!
> >
> > This is not a pressing issue.
> >
> > I am having trouble finding manufacturer's literature for above subject.
> > I want to know if, for example, listed for Seismic requires minimum
> > 4000 psi medium concrete and minimum diameter and length to see if I
> > can eliminate some of the options in 13 for prying factor and max
> > loads.
> >
> > Thanks,
> >
> > Brad
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkle
> > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZ
> > QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=yrdN
> > X83d8MbcZv8lzu7dg6zwjeaZ428y9qO9kIoWV0E&s=ks_1O-FpbukfZQZe5xBgbSung2IY
> > MLzznH0dcU6T0z0&e=
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.
> firesprinkler.org_listinfo.cgi_sprinklerforum-
> 2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_
> 2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=yrdNX83d8MbcZv8lzu7dg6zwjeaZ42
> 8y9qO9kIoWV0E&s=ks_1O-FpbukfZQZe5xBgbSung2IYMLzznH0dcU6T0z0&e=
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to