Does this pump supply any underground pipe, or 100% above-ground pipe?  

 

Ed Kramer

Bamford Fire

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Micah Davis, SET
Sent: Friday, June 15, 2018 8:50 AM
To: SprinklerForum <[email protected]>
Subject: Pump Discharge Piping

 

I have a fire pump installation that is having issues.  The contractor has
successfully completed a pump startup and test.  During a separate follow up
visit, the pump technician began having trouble getting the system back up
to maintenance pressure after fire pump operation.  The discharge piping has
an elbow between the pump and the discharge check valve.  It was first
suggested that this check valve was defective, so it was replaced.  The same
problem was experienced after this replacement.  It has been suggested that
the elbow directly after the pump is causing turbulence that is preventing
the check valve from closing properly.  I can find nothing in NFPA 20 or the
handbook to suggest this is a concern.  Have any of you seen this?  What
would your recommendation be?

 


Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV 

Dynamic Fire Designs


 


Mail: [email protected]
<mailto:[email protected]> 
Mobile: 931-242-1299
www.dynamicfiredesigns.com <http://dynamicfiredesigns.com>  


Dynamic Fire Designs . 13063 County Line Rd., Box #87 . Spring Hill . FL .
34609

This message is confidential. It may also be privileged or otherwise
protected by work product immunity or other legal rules. If you have
received it by mistake, please let us know by e-mail reply and delete it
from your system; you may not copy this message or disclose its contents to
anyone. The integrity and security of this message cannot be guaranteed on
the Internet. 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to