I'm doing a blast freezer that sits about 150 feet remotely from where the
riser is located.
I'm doing a DIPA with IRAS. If you really want to know, its a class 3
commodity stored in multiple-row racks 26' wide. Bldg is 25 feet to roof,
storage height is 20 feet.
This is in the northeast, so running ESFR is a non-starter.

This is being done under the 2013 edition of the code, and I'm having some
issues with trying to comply with the stuff in 7.9, especially 7.9.2.7

First, my DIPA requires the air tie-in to be fed from the system trim (DDX)
so using figure 7.9.2.7.1.1(a) is out. So my air supply run just doubled in
length.

Now, there are other freezers on the way to this freezer that are a lot
closer. Could I put my air lines in that freezer and still meet the intent
of 7.9.2.7, or is this going to be too confusing to have the ice plug check
lines in another location?

Please do not suggest relocating the pre-action valve closer to the
freezer, this isn't an option for the owner.


Secondly, who thought it was OK to allow nitrogen systems to only require
one ice plug check line? If the N2 system can't keep up with the demand or
has other issues it will start pumping in the same moist air direct from
its air compressor and be no different. I don't get that, but OK.

I'm pretty much 100% committed at this point to using a Dry Air Pack since
I don't have to run an intake line over to the cooler either. I haven't
seen anything on this being allowed on N2 systems unless they're listed for
freezer use. Does that exist?


Here's some other info:
We are also doing a dry system for a dry-goods storage warehouse that sits
next to the new freezer. Both are only connected to other freezers and
coolers on the property, so there is no other room or place to put our
valves besides the existing pump room. We are also running all this bulk
pipe outside! Mainly along exposed exterior building columns (don't know
how that happens, but I'm not going to look a gift horse in the mouth) and
then we will have to install a couple of pipe stands. This is all
galvanized, and will be the two mains: one for dry and one for DIPA. Owner
doesn't want DIPA for the dry goods warehouse because of detection and
expense for IRAS detection.

And of course, estimator didn't figure on running any extra air line piping
since he threw an N2 system on there! So no I'm trying to figure out a cost
efficient way of meeting the code on this one. Oh wait, isn't that what we
do every day anyway?

And hey, if you can't help me out on this one, no sweat (haha) and enjoy
our 4th of July tomorrow.!

Thanks all,
Ben Young


Benjamin Young
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to