How about a dry-barrel ESFR? Matt
From: Sprinklerforum <[email protected]> On Behalf Of Ben Young Sent: Tuesday, July 03, 2018 1:28 PM To: [email protected] Subject: Re: Airline feeds to freezers Mike, I assume you mean the V4603 25.2K upright, correct? That won't fly as the AHJ does not recognize FMG protection schemes unless they meet or exceed NFPA. Its a whole thing that will not likely change, so this is a non-option. Matt, You can use bottled nitrogen (and we were planning on doing that to initially fill the system instead of the quick fill on the N2 generator) but per my reading of 7.9.2.7 you still have to run a line thru the freezer for ice plug checks. I'm with you, it makes no sense since you should never see an ice plug with N2, but the code is the code. Benjamin Young On Tue, Jul 3, 2018 at 2:19 PM, Mike Stossel <[email protected]<mailto:[email protected]>> wrote: Ben, Would it help in anyway if you used the Victaulic LP46 heads? You maybe able to protect the freezers and the dry storage areas with the same dry pipe valve without in-rack sprinklers. Mike Stossel SET [400dpiLogoCropped] 36 Barren Road East Stroudsburg, PA 18302 Office: 973-670-2627 [email protected]<mailto:[email protected]> From: Sprinklerforum <[email protected]<mailto:[email protected]>> On Behalf Of Ben Young Sent: Tuesday, July 3, 2018 2:03 PM To: [email protected]<mailto:[email protected]> Subject: Airline feeds to freezers I'm doing a blast freezer that sits about 150 feet remotely from where the riser is located. I'm doing a DIPA with IRAS. If you really want to know, its a class 3 commodity stored in multiple-row racks 26' wide. Bldg is 25 feet to roof, storage height is 20 feet. This is in the northeast, so running ESFR is a non-starter. This is being done under the 2013 edition of the code, and I'm having some issues with trying to comply with the stuff in 7.9, especially 7.9.2.7 First, my DIPA requires the air tie-in to be fed from the system trim (DDX) so using figure 7.9.2.7.1.1(a) is out. So my air supply run just doubled in length. Now, there are other freezers on the way to this freezer that are a lot closer. Could I put my air lines in that freezer and still meet the intent of 7.9.2.7, or is this going to be too confusing to have the ice plug check lines in another location? Please do not suggest relocating the pre-action valve closer to the freezer, this isn't an option for the owner. Secondly, who thought it was OK to allow nitrogen systems to only require one ice plug check line? If the N2 system can't keep up with the demand or has other issues it will start pumping in the same moist air direct from its air compressor and be no different. I don't get that, but OK. I'm pretty much 100% committed at this point to using a Dry Air Pack since I don't have to run an intake line over to the cooler either. I haven't seen anything on this being allowed on N2 systems unless they're listed for freezer use. Does that exist? Here's some other info: We are also doing a dry system for a dry-goods storage warehouse that sits next to the new freezer. Both are only connected to other freezers and coolers on the property, so there is no other room or place to put our valves besides the existing pump room. We are also running all this bulk pipe outside! Mainly along exposed exterior building columns (don't know how that happens, but I'm not going to look a gift horse in the mouth) and then we will have to install a couple of pipe stands. This is all galvanized, and will be the two mains: one for dry and one for DIPA. Owner doesn't want DIPA for the dry goods warehouse because of detection and expense for IRAS detection. And of course, estimator didn't figure on running any extra air line piping since he threw an N2 system on there! So no I'm trying to figure out a cost efficient way of meeting the code on this one. Oh wait, isn't that what we do every day anyway? And hey, if you can't help me out on this one, no sweat (haha) and enjoy our 4th of July tomorrow.! Thanks all, Ben Young Benjamin Young _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
