I believe it was Viking and as far as I know they are still made.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
[email protected]<mailto:[email protected]>

From: Sprinklerforum <[email protected]> On Behalf 
Of Matt Grise
Sent: Tuesday, July 3, 2018 2:34 PM
To: [email protected]
Subject: RE: Airline feeds to freezers

Do they still make the ESFR that is specially listed for use with anti-freeze? 
I can’t remember who made that system…

Matt

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Ben Young
Sent: Tuesday, July 03, 2018 1:28 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Airline feeds to freezers

Mike, I assume you mean the V4603 25.2K upright, correct?
That won't fly as the AHJ does not recognize FMG protection schemes unless they 
meet or exceed NFPA. Its a whole thing that will not likely change, so this is 
a non-option.
Matt,
You can use bottled nitrogen (and we were planning on doing that to initially 
fill the system instead of the quick fill on the N2 generator) but per my 
reading of 7.9.2.7 you still have to run a line thru the freezer for ice plug 
checks.
I'm with you, it makes no sense since you should never see an ice plug with N2, 
but the code is the code.


Benjamin Young

On Tue, Jul 3, 2018 at 2:19 PM, Mike Stossel 
<[email protected]<mailto:[email protected]>> wrote:
Ben,

Would it help in anyway if you used the Victaulic LP46 heads?  You maybe able 
to protect the freezers and the dry storage areas with the same dry pipe valve 
without in-rack sprinklers.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
[email protected]<mailto:[email protected]>

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Ben Young
Sent: Tuesday, July 3, 2018 2:03 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Airline feeds to freezers

I'm doing a blast freezer that sits about 150 feet remotely from where the 
riser is located.
I'm doing a DIPA with IRAS. If you really want to know, its a class 3 commodity 
stored in multiple-row racks 26' wide. Bldg is 25 feet to roof, storage height 
is 20 feet.
This is in the northeast, so running ESFR is a non-starter.

This is being done under the 2013 edition of the code, and I'm having some 
issues with trying to comply with the stuff in 7.9, especially 7.9.2.7
First, my DIPA requires the air tie-in to be fed from the system trim (DDX) so 
using figure 7.9.2.7.1.1(a) is out. So my air supply run just doubled in length.
Now, there are other freezers on the way to this freezer that are a lot closer. 
Could I put my air lines in that freezer and still meet the intent of 7.9.2.7, 
or is this going to be too confusing to have the ice plug check lines in 
another location?
Please do not suggest relocating the pre-action valve closer to the freezer, 
this isn't an option for the owner.
Secondly, who thought it was OK to allow nitrogen systems to only require one 
ice plug check line? If the N2 system can't keep up with the demand or has 
other issues it will start pumping in the same moist air direct from its air 
compressor and be no different. I don't get that, but OK.
I'm pretty much 100% committed at this point to using a Dry Air Pack since I 
don't have to run an intake line over to the cooler either. I haven't seen 
anything on this being allowed on N2 systems unless they're listed for freezer 
use. Does that exist?
Here's some other info:
We are also doing a dry system for a dry-goods storage warehouse that sits next 
to the new freezer. Both are only connected to other freezers and coolers on 
the property, so there is no other room or place to put our valves besides the 
existing pump room. We are also running all this bulk pipe outside! Mainly 
along exposed exterior building columns (don't know how that happens, but I'm 
not going to look a gift horse in the mouth) and then we will have to install a 
couple of pipe stands. This is all galvanized, and will be the two mains: one 
for dry and one for DIPA. Owner doesn't want DIPA for the dry goods warehouse 
because of detection and expense for IRAS detection.
And of course, estimator didn't figure on running any extra air line piping 
since he threw an N2 system on there! So no I'm trying to figure out a cost 
efficient way of meeting the code on this one. Oh wait, isn't that what we do 
every day anyway?
And hey, if you can't help me out on this one, no sweat (haha) and enjoy our 
4th of July tomorrow.!
Thanks all,
Ben Young


Benjamin Young

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to