You can include the city supply.  I typically set a fire pump up at the 
exterior of the building at the FDC location



Mike Stossel SET



36 Barren Road

East Stroudsburg, PA 18302

Office: 973-670-2627

 <mailto:[email protected]> [email protected]



From: Sprinklerforum <[email protected] 
<mailto:[email protected]> > On Behalf Of Jerry 
Van Kolken
Sent: Friday, August 24, 2018 4:23 PM
To: [email protected] 
<mailto:[email protected]>
Subject: RE: Fire Truck Supply @ FDC



Is it just 150psi or is it 150 + city supply?



Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722



From: Sprinklerforum [ <mailto:[email protected]> 
mailto:[email protected]] On Behalf Of Bruce Verhei
Sent: Monday, September 12, 2016 2:19 PM
To:  <mailto:[email protected]> 
[email protected]
Subject: Re: Fire Truck Supply @ FDC



Oh, and starting at something lower than eventual EP is more than adequate to 
let you find open standpipe ports, and close them. Why flood the stairwell more 
than necessary?



BV


On Sep 12, 2016, at 14:06, Bruce Verhei <[email protected] 
<mailto:[email protected]> > wrote:

Most FD's use 150 psi as a near universal starting point. It's what an FDC 
basically says "start me at".



If nozzle is not too high above FDC this isn't too bad. If nozzle is a number 
of floors up the operator will be ready to provide water before its needed. And 
it gets all of the now compressed air out of the system.



But once water is flowing, the pump operator will do field calc's to get the 
appropriate real pressure. Our standard 1 3/4 hose packs used 135 psi for 
friction loss and nozzle pressure. I suspect cities with bigger footprint 
buildings would use a 200' instead of 150' hose pack, getting you back to ~150 
psi at gated wye (2 1/2" X 1 1/2" X 1 1/2") I know an alternative is 50' 2 1/2" 
then wye, then standpipe bundles.



Our standard was for head pressure was 5 psi per floor. For all you three 
significant digit folks, this actually works out pretty close for 10-12' 
storeys.



Field calc also includes friction loss between engine and FDC.



And our standard calc included 25 psi for friction loss in the standpipe 
system. I later decided that this was way too much, but fire experience belied 
the numbers. The scheme we used did not result in too high nozzle pressure. 
Usually more pressure was requested by radio. Eventually I decided that hose 
lines were much more liable to have kinks in this setting compared to homes, 
restaurants, repair garages and so on. Compare a kink to a 1" 90 in a 1 1/2" 
sprinkler line. Lots of friction loss in a very short run.



So I didn't send a note to Training telling them no, we weren't seeing 25 psi 
f.l. in a five story standpipe at 200 gpm.



NP + attack line FL + HP + 25 for standpipe and FDC + FL from engine to FDC = EP



To recap,

-150 psi to get water flowing,

-connect second 2 1/2" line to FDC and get it charged,

-do field hydraulics, increase engine pressure, and reset relief valve ( or 
governor)

-adjust up 20 psi per each request from attack companies. 20 psi is about 
minimum that is noticeable. During active fire fighting you will not get a 
request for less.



After control, at some point pressure will be adjusted way down, per request.



This is one FD's practice. It works well in low rise.



Best



Bruce Verhei



On Sep 12, 2016, at 13:00, Brian Harris <[email protected] 
<mailto:[email protected]> > wrote:

Thanks guys, much appreciated.



Brian Harris, CET

BVS Systems Inc.

bvssytemsinc.com <http://bvssystemsinc.com/>



From: Sprinklerforum [ <mailto:[email protected]> 
mailto:[email protected]] On Behalf Of Brian Harris
Sent: Monday, September 12, 2016 3:21 PM
To:  <mailto:[email protected]> 
[email protected]
Subject: Fire Truck Supply @ FDC



Is there a “standard” GPM @ PSI used for a standpipe calc with regard to what 
the fire truck will provide? I called the local AHJ and all he would say is 
they provide 150psi, didn’t know the gpm or even the hose size for that matter. 
Any help would be greatly appreciated.



Brian Harris, CET

BVS Systems Inc.

Design Manager

 <http://bvssystemsinc.com/> bvssystemsinc.com

Phone: 704.896.9989

Fax: 704.896.1935



_______________________________________________
Sprinklerforum mailing list
 <mailto:[email protected]> 
[email protected]
 <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to