175 is not out of reason at all, whether manual or automatic.  You do need to 
make sure you don’t exceed pressure ratings of the components.  Also, for 
traditional 150# systems that we hydro to 200# for, you would need to increase 
your test pressure to 50# over.  I see that all the time.  On thing I’ve been 
discussing with local AHJ’s is the placard.  How is a pump operator going to 
know what pressure is at the FDC?  I think we should be calculating loss 
through how ever much discharge needed for a pumper parked at the hydrant 
(within 150’) and the placard state discharge pressure at the piece, not the 
FDC.  I put a gauge on the FDC when using an outside pumper but operations 
aren’t going to change telling FF to install a good gauge and watch it 150’ 
away.

Just my $0.02.

TD

 

From: Sprinklerforum <[email protected]> On Behalf 
Of Kyle.Montgomery
Sent: Monday, August 27, 2018 2:37 PM
To: [email protected]
Subject: RE: Fire Truck Supply @ FDC

 

Now that’s what I’m looking for.

 

So requiring a pressure up to 175 psi should be no big deal (adjustments for 
pressure to below grade levels not withstanding), but 175 psi should be the 
practical limit. Would you agree?

 

Thanks, Pete.

 

-Kyle M