That makes sense. I don't think testing at 225 psi would be a big deal, 
although I could definitely see someone forgetting to do that.

As far as Tom's comments about the placard, I understand it, but I'm wondering 
how much this really matters from a practical standpoint (I obviously have zero 
experience manually fighting a fire). Could the operator not start out at 150 
psi, and if the guy on the end of the hose needs more pressure, he just radios 
for some more pressure? That's the part that I'm missing, because it seems like 
the fire department would simply make adjustments to the pressure they are 
supplying based on need, regardless of what the placard says. Is it more 
complex than that in the field?

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Monday, August 27, 2018 12:21 PM
To: [email protected]
Subject: [EXTERNAL] Re: Fire Truck Supply @ FDC

175 is convenient, yes, so long as you test to +50 psi. For whatever it is 
worth, I have not yet met a fire official who wouldn't approve a design that 
requires up to 175 psi inlet pressure for a building not classified as 
high-rise.

Steve L.
Get Outlook for 
Android<https://urldefense.proofpoint.com/v2/url?u=https-3A__aka.ms_ghei36&d=DwMF-g&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=rd4JA7vQ1D7QJHEZ83zE-cy5yO0riGIhGpXWnmkRaOA&s=47ahl_fVc6N49Y_46Zu9z_qEjHIUeLLjAzeIob7gF7E&e=>

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Tom Duross <[email protected]<mailto:[email protected]>>
Sent: Monday, August 27, 2018 2:51:52 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Fire Truck Supply @ FDC

175 is not out of reason at all, whether manual or automatic.  You do need to 
make sure you don't exceed pressure ratings of the components.  Also, for 
traditional 150# systems that we hydro to 200# for, you would need to increase 
your test pressure to 50# over.  I see that all the time.  On thing I've been 
discussing with local AHJ's is the placard.  How is a pump operator going to 
know what pressure is at the FDC?  I think we should be calculating loss 
through how ever much discharge needed for a pumper parked at the hydrant 
(within 150') and the placard state discharge pressure at the piece, not the 
FDC.  I put a gauge on the FDC when using an outside pumper but operations 
aren't going to change telling FF to install a good gauge and watch it 150' 
away.
Just my $0.02.
TD

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Kyle.Montgomery
Sent: Monday, August 27, 2018 2:37 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Fire Truck Supply @ FDC

Now that's what I'm looking for.

So requiring a pressure up to 175 psi should be no big deal (adjustments for 
pressure to below grade levels not withstanding), but 175 psi should be the 
practical limit. Would you agree?

Thanks, Pete.

-Kyle M