The likelihood and cost/benefit analysis is a debate that should be happening 
at the building code development and adoption phases when determining what the 
minimum code requirements should be in the building codes and standards.

You may want to consider that public buildings that are funded by taxpayers are 
a community investment of resources which should be protected against fire and 
other hazards to be more resilient and durable to make the most of the 
investment of community resources, especially since reconstructing a new public 
building in future dollars is generally more expensive.  Fire and other natural 
disasters like earthquakes can be a low likelihood event when considering 
building code requirements, but when it happens, we don't want to rebuild from 
scratch, especially when it comes to big buildings and important buildings.  
Fires can also be an immediate secondary event after an earthquake where 
multiple simultaneous fires occur to add to the chaos and destruction with 
emergency services stretched thin... and other things like this happen as 
reported at 
http://www.historynet.com/the-great-1906-san-francisco-earthquake-and-fire.htm: 
 "One of the first casualties was Fire Chief Engineer Dennis T. Sullivan, who 
was mortally wounded when a chimney from the California Theater smashed without 
warning into the fire station where he was living. The fire department, faced 
with the greatest crisis in its history, was effectively decapitated."

Predicting how owners will actually use the building and what future contents 
will be in the building is hard.  I would point out that in many cases, public 
school buildings that were not designed as emergency shelters are often used as 
emergency shelters and can be found with various other potentially 
unanticipated uses ranging from voting stations to weekend religious services 
to student sleep-ins.  I would also highlight that NFPA 13 annex guidance on 
storage commodity classifications finally/recently changed to catch up with the 
reality of modern storage and packaging due to the uses of higher BTU plastics 
replacing the traditional materials prevalent when the previous annex guidance 
was first put in the standard.

On a relate note, we have even had difficulties in the past convincing some 
local jurisdictions that resisted protecting fire stations with fire sprinklers 
when the building codes clearly require them to be sprinklered [when budget 
concerns and possibly some fire service hubris combined].  We had to educate 
them on both the legal requirements and the reasoning behind the code 
requirements and the political reality of trying to get it rebuilt if it did 
burn down after we had told them it was required to be protected by 
sprinklers...  PS:  Google fires in fire stations to get link to articles like 
this:  http://mentalfloss.com/article/22704/do-fire-stations-ever-catch-fire

Respectfully,

David Blackwell

David Blackwell, P.E.
Chief Engineer
(803)896-9833

Office of State Fire Marshal
141 Monticello Trail | Columbia, SC 29203
http://statefire.llr.sc.gov/
(803)896-9800

"Our firefighting starts with plan review..."

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of å... ....
Sent: Sunday, October 28, 2018 1:18 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: High School Weight Room - epistemology of fire hazard classification

*** SCDLLR NOTICE ***
•  This email is from an external email address. Please use caution when 
deciding whether to open any attachments or when clicking links.
•  Personally Identifiable Information (PII) should not be included in e-mail 
text or attachments. Do not save or transmit PII unencrypted.



I doubt LH at top of gym ceiling will control rolled up mats of PU/expanded 
foam.. Even with over pressure.

Now, if we want to design MORE EXPLICITLY by risk analyses
     (and consider  ignition likelihood... [or just use the words "cauase and 
origin" to get hits when lawyers conduct expert witness searches" ])
let us go there.

Consider:  how many of our Electronic Equipment or Information Technology rooms 
with pre-action systems are in
such a state of readiness that they will control their design fire?     Design 
being:  density over area

 Answer:  maybe, maybe...  3/4 of SIPA systems in N. America (includes Mexico) 
which are 7-years on from commissioning, will be able to control their design 
fire.
  Essentially 25+% of owners are running without any active, automatic  fire 
protection in these occupancies...
  So by previous logic applied to defend LH in school gyms, since fires are not 
a big problem in Information Technology rooms,
  (at least not a big enough problem that they are a current industry concern 
of note) we could  then
  not put ANY pre-action SIPA sprinklers in Intformation Technology rooms 
because many of these rooms essentially don't have working sprinklers.
  And this has not created a problem of note.

Use of  risk analyses would make a LOT of our fire protection work goes away.
Fire is rare.
It is not because our "fancy bling-bling fire systems" (e.g. "dirty agent gas 
systems marketed as clean agent; SIPA, DIPA, ) are so reliable that we have 
tolerable fire losses.
It is because Mr. Fire comes to town so seldom, in these occupancies, that we 
have tolerable losses..

Yes, school students should be able to evacuate a sprinklered gymnasium before 
untenable fire conditions develop.
Risk analyses should show these students are able to evacuate safely even 
without a sprinkler system.
And yes, ignition is extremely infrequent in schools.
But these risk arguments fuel a decision for NO sprinklers, not an argument to 
install sprinklers using less water delivery.
The PU mats in the gym (especially mats oriened vertically) represent a fire 
hazard well beyond LH.

Is flexible foam in a gym different than flexible foam in movie theater seating?
A gym can serve different purposes (tupperware bake sales);  a movie theatre is 
less versatile.
Come to think of it, if a fire developed in several movie theatre flexible foam 
seats (a very implausible scenario)
       I doubt LH would control such a fire in a theater, especially with 
pitched rows of seating.
       The radiative feedback created by the row-seating enclosure would aid 
fire spread.
But fire is so rare there, we don't care.

NFPA 13 currently focusses mostly on fire hazard.  It design to the hazard.
If we want to design to the likelihood, that is fine and an advancement of the 
art that I welcome.

NFPA 13, 25 and the Building Code seldom address explicitly:  fire risk 
analyses,  likelihoods of ignition and likelihoods of RAM.
They should do this more.  And they should include more cost implications.
It is realized keeping sprinkler costs down is a real concern to maintaining an 
income in fire protection.  It is a conern because many
owners and clients realize that Mr. Fire is an infrequent visitor.  Thus they 
make their own risk analyses and pressure designers to
value engineer the fire protection budget downwards.

Risk analyses is local, because risk tolerance is local
That is why when making a risk based assumption (and virtually all design 
decisions of consequence are risk based),
the assumptions SHOULD be memorialized on the drawing, next to the design guide 
citations.
Really important design decisions should be memorialized on metal plaques and 
sunk into the wall at the building entry, with stakeholders names.

Unfortunately, we usually don't mention the decision rational explicitly, 
burying the decision trail under mounds of detail instead.
    Then when the fatalities happen (not in said gyms), we pay SMEs who write 
the safety codes to sift through the ashes of buried details.

As resources become tighter, and they are at an ever accelerating rate,  we 
must lean more and more on good judgment and local risk tolerance.

Application of  NFPA 13 on a hazard analyses, suggest to me, that flexible foam 
gymnasium wrestling (not joga) mats pose a higher sprinkler hazard than LH.
If we want to couch our design using risk analyses, then declare the risk 
analyses logic up front on our General Notes, next to the design guide 
citations.

That is why THIS forum is so valuable.  This forum openly debates the details.
And it is that process of open discussion, which helps us make better future 
decisions.


Notes:
1.  I don't make money as an expert witness in court.
2.  I do design sprinkler systems from soup to nuts, but my current clients 
focus on saving money in areas with larger returns ( ITM on MEP utilites) than 
saving a little money on sprinkler capitalization costs.



Scot Deal
Excelsior Risk & Fire Engineering
gms:  +420 606 872 129  (GMT + 2)