Not personally but I know we put a lot of them in.  More generally, for 
the higher application (40' ceiling) the difference is not as big since 
the UL listing pressure is lower, it's still about 150 gpm more.  With 
most of the designs we do today the hose stream is rarely a big issue 
because of how flat pump curves are with many of the newer models and it 
rarely flows though anything other than 10-12" underground loops.. As far 
as the FM criteria, that's between you and your contract holder and you 
and the AHJ.  If your project is a design build you should be able to 
employ any technology/design that results in an "approved" system.  If the 
head was spec'd without design parameters you may want to RFI to CYA.  As 
for AHJ approval, for example here in Indiana state virtually always 
accepts FM designs as new/alternative technology.


The views, opinions and judgements expressed in this message are solely 
those of the author.  The message contents have not been revewed or 
approved by S&S
Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]







From:   Tony Silva <[email protected]>
To:     [email protected]
Date:   11/07/2018 07:41 PM
Subject:        Victaulic LP4601
Sent by:        "Sprinklerforum" 
<[email protected]>



BE ADVISED - This email originated outside EMCOR. 


Has anyone used this k25 storage sprinkler? It has listing for both UL and 
FM. UL lists it as a CMSA sprinkler whereas FM listing is for standard 
coverage resulting in the UL design requirements being more stringent. 
Example, UL requires 15 sprinkler design with 500 gpm hose allowance. FM 
requires 12 sprinkler design with 250 hose allowance. My question is, can 
the design comply with FM and not UL, even though the contract 
specifications doesn't require FM compliance?

Tony_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=Sz4IVtNPCaGN1ntc6APphjZeXUc10P3Bxoni2s-_dVE&s=JUwe0hyyCM3IvIWb9oq7ljr4PcJkbWYhpaw9cxO-CTI&e=




This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to