So, in that case, would they be required to eliminate the non-indicating gate 
valve? Or just add the PIV? I mean, if the gate valve is closed, it really 
doesn’t matter what position the PIV is in.

I know there are some jurisdictions in Nevada where we’ve been required to 
provide wall PIVs for the system control valves. But I’m not 100% certain what 
their intent was in requiring it. Is it about knowing if the valve is open or 
closed, or is it about being able to control it from the building exterior?

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Prahl, Craig/GVL
Sent: Monday, December 3, 2018 2:27 PM
To: [email protected]
Subject: RE: [EXTERNAL] Re: RE: PIV

NFPA 24 calls for indicating type valves on water supplies serving sprinklers.  
Non-indicating type valves for sprinkler water control are permitted only when 
approved by the AHJ.  So it’s totally within the right of the AHJ to require a 
PIV outside the room on the UG run-in.

In some cases when there is no place to install a PIV, sometimes the AHJ has 
allowed a Wall Post Indicator Valve to be used.

Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.jacobs.com_&d=DwMGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=W5k1qnXz5UTLiUTVBFXf1ukUHVZP7Ml_5hDoOndgGKU&s=1RIIM_z8a8cOpL0DI30l1AnTsqSGUZCFy54U0touGCk&e=>

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Bruce Verhei
Sent: Monday, December 03, 2018 3:47 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] Re: RE:

To follow JD’s comment, new or existing would to me be the big question.  Or 
said another way, if new, why weren’t approved plans followed?

Best.

Bruce Verhei

On Dec 3, 2018, at 12:10, Matt Grise 
<[email protected]<mailto:[email protected]>> wrote:
There is a city we work in where every building must have a PIV. I don’t know 
if that is in the code, but the fire department won’t approve a system without 
one.

Matt

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Randy Huffman
Sent: Monday, December 03, 2018 2:06 PM
To: 
[email protected]<mailto:[email protected]>
Subject:

We have a riser room at the rear of a building. An exterior door opens to 
interior of riser room which contains a backflow preventer with two indicating 
control valves, a rise check valve, and a water flow switch. Underground line 
to building has a nonindicating gate valve in roadway box some distance from 
door to riser room. AJH says a post indicator valve must be installed outside 
riser room. We believe the current arrangement of piping and valves meets the 
standard without the PIV
Please comment.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=lXsJUcku6Cs3Ph_G1QTW4M6ffWMQo2QFYsrknTByiwQ&s=_JVHbOtWOq8UdJrV7L3LmA-ftMxo9n8OgtXbU7rfkek&e=>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.