When you step through the changes over the years in NFPA regarding the roadway box setup for fire protection service you will notice there was a change a couple of years back that eliminated the AHJ’s prerogative to demand the post indicator setup. The wording change is subtle but it definitely removed the AHJ's prerogative as if that was the change’s specific intent. That is how I recall it. I do not believe this has ever been mentioned here. Good luck convincing the dyed-in-the-wool followers who are used to a former standard that one might figure was too basic to ever get changed. Keep in mind there are some cities with an ordinance that straight up requires the PIV setup.
Allan Seidel St. Louis, MO > On Dec 3, 2018, at 3:26 PM, Prahl, Craig/GVL <[email protected]> wrote: > > NFPA 24 calls for indicating type valves on water supplies serving > sprinklers. Non-indicating type valves for sprinkler water control are > permitted only when approved by the AHJ. So it’s totally within the right of > the AHJ to require a PIV outside the room on the UG run-in. > > In some cases when there is no place to install a PIV, sometimes the AHJ has > allowed a Wall Post Indicator Valve to be used. > > Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | > [email protected] <mailto:[email protected]> | www.jacobs.com > <http://www.jacobs.com/> > > From: Sprinklerforum <[email protected]> On > Behalf Of Bruce Verhei > Sent: Monday, December 03, 2018 3:47 PM > To: [email protected] > Subject: [EXTERNAL] Re: RE: > > To follow JD’s comment, new or existing would to me be the big question. Or > said another way, if new, why weren’t approved plans followed? > > Best. > > Bruce Verhei > > On Dec 3, 2018, at 12:10, Matt Grise <[email protected] > <mailto:[email protected]>> wrote: > > There is a city we work in where every building must have a PIV. I don’t know > if that is in the code, but the fire department won’t approve a system > without one. > > Matt > > From: Sprinklerforum <[email protected] > <mailto:[email protected]>> On Behalf Of Randy > Huffman > Sent: Monday, December 03, 2018 2:06 PM > To: [email protected] > <mailto:[email protected]> > Subject: > > We have a riser room at the rear of a building. An exterior door opens to > interior of riser room which contains a backflow preventer with two > indicating control valves, a rise check valve, and a water flow switch. > Underground line to building has a nonindicating gate valve in roadway box > some distance from door to riser room. AJH says a post indicator valve must > be installed outside riser room. We believe the current arrangement of piping > and valves meets the standard without the PIV > Please comment. > _______________________________________________ > Sprinklerforum mailing list > [email protected] > <mailto:[email protected]> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=lXsJUcku6Cs3Ph_G1QTW4M6ffWMQo2QFYsrknTByiwQ&s=_JVHbOtWOq8UdJrV7L3LmA-ftMxo9n8OgtXbU7rfkek&e=> > > NOTICE - This communication may contain confidential and privileged > information that is for the sole use of the intended recipient. Any viewing, > copying or distribution of, or reliance on this message by unintended > recipients is strictly prohibited. If you have received this message in > error, please notify us immediately by replying to the message and deleting > it from your computer. > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org