I AM 8' OFF SIDE WALL AND 17'6 OFF FAR WALL. WITH A HSW

 

BUT SINCE ROOM IS LESS THAN 800 SQFT.

 

I CAN USE THE ACTUAL ROOM SQUARE FOOTAGE. WHICH IS 210 SQFT.

 

WHICH THEN SAYS 21.0 GPM. THEN DETERMINE PSI WITH WHATEVER K-FACTOR IS CHOSEN. 
COMPARE THE 21 GPM TO THE LISTED REQUIREMENTS AND USE THE GREATER OF THE 2.

 

ANYONE DISAGREE?

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of cw bamford
Sent: January-07-19 1:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: residential sprinklers

 

For 18 x 18   use a 5.8 K 1/2" NPT  or  7.6 K   3/4" NPT

 

and please check the S x L rule(s) maybe you are 9' off 1 wall and 8' off the 
other

for a   18 x 16 spacing =  288 sq ft

 

Chuck Bamford SET

 

On Mon, Jan 7, 2019 at 10:02 AM Trillium Fire Sprinkler Design Inc. 
<trilliumf...@cwisp.ca> wrote:

YES. I HAVE MANY OPTIONS. I JUST WANTED TO MAKE SUE I WAS READING THE CODE 
PROPERLY.

 

THANKS FOR THE CONFIRMATION.

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Fpdcdesign
Sent: January-07-19 12:57 PM
To: Sprinklerforum
Subject: Re: residential sprinklers

 

WHy not use a K5.6 residential sprinkler?


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (ofc)

860-553-3553 (fax)

860-608-4559 (cell)





On Jan 7, 2019 at 12:53 PM, <Steve Leyton <mailto:st...@protectiondesign.com> > 
wrote:

Sorry ‘bout that last one.

 

Assuming you stretch the spacing to 18’ x 18’ your math is correct.  But you 
don’t have to assume maximum listed areas of coverage, you use the actual S x 
L.  If a residential sprinkler is spaced so that its area of coverage is 14’ x 
16’-9”, you have to use a sprinkler that’s listed up to 18’ x 18’, but you 
would calculate the discharge at 23.45 gpm.    

 

Steve L.

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Trillium Fire Sprinkler Design Inc.
Sent: Monday, January 07, 2019 9:50 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: residential sprinklers

 

I HAVE A HOTEL THAT SAYS NFPA 13 DESIGN.

 

IF I USE RESIDENTAIL SPRINKLERS IN THE UPPER FLOORS. AM I CORRECT IN SAYING 
THAT I MUST USE .10 DESNITY

 

EXAMPLE . I WAS GOING TO USE 18x18 4.9 K SPRINKLER

 

REQUIRES 17 GPM @ 12 PSI FOR .05 DENSITY

 

BUT SINCE NFPA #13 WOULD I BE REQUIRED TO DESIGN TO THESE NUMBERS.  32.4 GPM @ 
43.72 PSI?

 

OR AM I MISSING SOMETHING.

 

THANKS

 

 

_______________________________________________ Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to