I AM 8' OFF SIDE WALL AND 17'6 OFF FAR WALL. WITH A HSW
BUT SINCE ROOM IS LESS THAN 800 SQFT. I CAN USE THE ACTUAL ROOM SQUARE FOOTAGE. WHICH IS 210 SQFT. WHICH THEN SAYS 21.0 GPM. THEN DETERMINE PSI WITH WHATEVER K-FACTOR IS CHOSEN. COMPARE THE 21 GPM TO THE LISTED REQUIREMENTS AND USE THE GREATER OF THE 2. ANYONE DISAGREE? From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of cw bamford Sent: January-07-19 1:20 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: residential sprinklers For 18 x 18 use a 5.8 K 1/2" NPT or 7.6 K 3/4" NPT and please check the S x L rule(s) maybe you are 9' off 1 wall and 8' off the other for a 18 x 16 spacing = 288 sq ft Chuck Bamford SET On Mon, Jan 7, 2019 at 10:02 AM Trillium Fire Sprinkler Design Inc. <trilliumf...@cwisp.ca> wrote: YES. I HAVE MANY OPTIONS. I JUST WANTED TO MAKE SUE I WAS READING THE CODE PROPERLY. THANKS FOR THE CONFIRMATION. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Fpdcdesign Sent: January-07-19 12:57 PM To: Sprinklerforum Subject: Re: residential sprinklers WHy not use a K5.6 residential sprinkler? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell) On Jan 7, 2019 at 12:53 PM, <Steve Leyton <mailto:st...@protectiondesign.com> > wrote: Sorry ‘bout that last one. Assuming you stretch the spacing to 18’ x 18’ your math is correct. But you don’t have to assume maximum listed areas of coverage, you use the actual S x L. If a residential sprinkler is spaced so that its area of coverage is 14’ x 16’-9”, you have to use a sprinkler that’s listed up to 18’ x 18’, but you would calculate the discharge at 23.45 gpm. Steve L. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Trillium Fire Sprinkler Design Inc. Sent: Monday, January 07, 2019 9:50 AM To: sprinklerforum@lists.firesprinkler.org Subject: residential sprinklers I HAVE A HOTEL THAT SAYS NFPA 13 DESIGN. IF I USE RESIDENTAIL SPRINKLERS IN THE UPPER FLOORS. AM I CORRECT IN SAYING THAT I MUST USE .10 DESNITY EXAMPLE . I WAS GOING TO USE 18x18 4.9 K SPRINKLER REQUIRES 17 GPM @ 12 PSI FOR .05 DENSITY BUT SINCE NFPA #13 WOULD I BE REQUIRED TO DESIGN TO THESE NUMBERS. 32.4 GPM @ 43.72 PSI? OR AM I MISSING SOMETHING. THANKS _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org