NFPA 2013 2019 - 11.3.2 (8) Extended coverage sprinklers installed to 
protect areas below a single overhead door(s)

that should cover you



Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]







From:   Skyler Bilbo <[email protected]>
To:     [email protected]
Date:   04/05/2019 02:31 PM
Subject:        EC HSW Under Garage Doors
Sent by:        "Sprinklerforum" 
<[email protected]>



BE ADVISED - This email originated outside EMCOR. 

Is anyone installing EC HSW heads under garage doors?  I keep running into 
16 ft wide doors (queue jokes: "just open the door").  It would be cheaper 
to install one EC head rather than a standard spray HSW on each side.  

I'm looking in the 2013 version of NFPA 13, and I see in 8.4.2 where it 
allows standard sidewall spray sprinklers under garage doors, which isn't 
mentioned for the similar section regarding extended coverage sidewall 
sprinklers.  It is mentioned in the EC HSW section: 8.9.5.3.2 that 
sprinklers are required under obstructions over 4 ft wide such as overhead 
doors.  I'm thinking this is just saying sprinklers are required under the 
garage door due to the obstruction, but not implying that EC HSW can be 
used.  It seems to me that NFPA is already being "nice" to us by letting 
us use the Light Hazard spacing for these HSW heads under garage doors and 
spacing the heads out farther with EC heads is pretty liberal if you are 
worried about this head ever actually going off in a fire.  I would be 
interested to know if there has been any testing on this.


Thanks,
Skyler Bilbo_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=JfddSnRHvASLscCAQ7fPAc_hWOQTMOTCFlULHkBP3wY&s=MCa_hXG8oPD-5QoSupXxx745eXtTyBzVQhCP6FRC0z8&e=




This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to