Hi Skyler:

I think you are putting too much thought into the matter. You had it covered 
when you read NFPA 13-2013,  Section 8.9.5.3.2: “Sprinklers shall be installed 
under fixed obstructions over 4 ft (1.2 m) wide, such as ducts, decks, open 
grate flooring, cutting tables, and overhead doors.”

Since Section 8.9 is for Extended Coverage Sidewall Spray Sprinklers, there is 
really no question – they are okay to use there.

Larry Keeping

From: Sprinklerforum <[email protected]> On Behalf 
Of Skyler Bilbo
Sent: April-05-19 2:52 PM
To: [email protected]
Subject: Re: EC HSW Under Garage Doors

Thanks!  I need to buy the 2019 version...  I feel like one of those old guys, 
from when I started in the industry, that quotes older versions because those 
are the ones I'm most familiar with... I'm not looking forward to learning the 
new rearranged chapters but I also don't want to be "that guy" who needs to get 
with the times.  Times are definitely changing when a millennial starts having 
old person dilemmas, haha.


Skyler Bilbo


On Fri, Apr 5, 2019 at 1:35 PM Mike B Morey 
<[email protected]<mailto:[email protected]>> wrote:
NFPA 2013 2019 - 11.3.2 (8) Extended coverage sprinklers installed to protect 
areas below a single overhead door(s)

that should cover you

________________________________

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]<mailto:[email protected]>

[cid:[email protected]]





From:        Skyler Bilbo 
<[email protected]<mailto:[email protected]>>
To:        
[email protected]<mailto:[email protected]>
Date:        04/05/2019 02:31 PM
Subject:        EC HSW Under Garage Doors
Sent by:        "Sprinklerforum" 
<[email protected]<mailto:[email protected]>>
________________________________



BE ADVISED - This email originated outside EMCOR.

Is anyone installing EC HSW heads under garage doors?  I keep running into 16 
ft wide doors (queue jokes: "just open the door").  It would be cheaper to 
install one EC head rather than a standard spray HSW on each side.

I'm looking in the 2013 version of NFPA 13, and I see in 8.4.2 where it allows 
standard sidewall spray sprinklers under garage doors, which isn't mentioned 
for the similar section regarding extended coverage sidewall sprinklers.  It is 
mentioned in the EC HSW section: 8.9.5.3.2 that sprinklers are required under 
obstructions over 4 ft wide such as overhead doors.  I'm thinking this is just 
saying sprinklers are required under the garage door due to the obstruction, 
but not implying that EC HSW can be used.  It seems to me that NFPA is already 
being "nice" to us by letting us use the Light Hazard spacing for these HSW 
heads under garage doors and spacing the heads out farther with EC heads is 
pretty liberal if you are worried about this head ever actually going off in a 
fire.  I would be interested to know if there has been any testing on this.


Thanks,
Skyler Bilbo_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=JfddSnRHvASLscCAQ7fPAc_hWOQTMOTCFlULHkBP3wY&s=MCa_hXG8oPD-5QoSupXxx745eXtTyBzVQhCP6FRC0z8&e=
This message is for the named person's use only. It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission. If you receive this message in error, 
please immediately delete it and all copies of it from your system, destroy any 
hard copies of it and notify the sender. You must not, directly or indirectly, 
use, disclose, distribute, print, or copy any part of this message if you are 
not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to