Yes.

FM provided me some internal information maybe twenty years ago. Typical 
scenario is all heads operate. From building, mechanical, and fire code a paint 
spray booth is no a separate occupancy class, it is a piece of equipment for 
special purpose, with
specific requirements. Among other things this is how you can have a simple 
layer of metal instead of a rated fire resistive wall, and too narrow for 
normal personnel doors.

Paint Rooms are different. There are put in a Hazardous Occupancy Class. 

Careful when you cross from model codes to sprinkler standard.

Best.

Bruce Verhei 

> On Apr 23, 2019, at 09:48, Matt Grise <[email protected]> wrote:
> 
> Regarding the paint booth – It is listed as a specially occupancy and it 
> specifically says that the water supply shall be sufficient to supply all 
> sprinklers likely to open in one event (13-2016 22.4.1.3). Based on that, is 
> it required to add the extra gpm to the supply main for a small booth? In the 
> 6-head-booth instance, could you say that 6 heads are likely to open, 
> therefore supply water for 6 heads plus hose lines (not the full EH2 flow)?
>  
> Matt
>  
>  
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Roland Huggins
> Sent: Tuesday, April 23, 2019 11:11 AM
> To: [email protected]
> Subject: Re: Intent of 23.4.4.2.5
>  
> There is also the option to have a remote area with different hazard 
> classifications within it (and the size of it is predicated upon whether 
> there are walls around the smaller, higher hazard portion).  Look at A.11.1.2.
>  
>  
> Roland
>  
> 
> Roland Huggins, PE
> Senior Vice President, Engineering & Technical Services
> American Fire Sprinkler Association
> p:
> 214-349-5965 ext121
> w:
> firesprinkler.org  
>       
> 4 days. 1,500+ attendees.
> AFSA38: Convention, Exhibition, & Apprentice Competition is North America's 
> largest fire sprinkler trade event. Join us at the Manchester Grand Hyatt in 
> beautiful San Diego, California October 1-4, 2019. Priority booth selection 
> starts April 12. Get yours now. MORE INFO
> 
> 
> On Apr 23, 2019, at 8:55 AM, Travis Mack, SET, CFPS, CWBSP, RME-G 
> <[email protected]> wrote:
>  
> I’ve run into a few AHJs that have specifically thrown this section to us for 
> paint booths.  We also had this thrown at us on a tire carousel storage.  
> This caused total havoc on the projects.
>  
> The paint booth was in an existing facility designed to OH2.  They paint 
> booth had 6 sprinklers.  We had to run a 6” bulk across the facility to get 
> this paint booth.  It seems like overkill, but following that section as it 
> is written, we had to flow 800 gpm for the area. 
>  
> <image002.jpg>
> Travis Mack, CFPS, CWBSP, RME-G, SET
> MFP Design, LLC
> 3356 E Vallejo Ct
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> [email protected]
> www.mfpdesign.com
>  
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>  
> “The bitterness of poor quality remains long after the sweetness of low price 
> is forgotten.”
>  
>  
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Bruce Verhei
> Sent: Tuesday, April 23, 2019 8:17 AM
> To: [email protected]
> Subject: Re: Intent of 23.4.4.2.5
>  
> I read it as Ed notes. As well other example of paint spray booth I’d 
> question too. Paint spray booths can have sprinkler protection in an 
> otherwise unsprinklerd building. They’d all be dry chem total flood if we 
> drove an underground sized up that much. Just the cost of larger DDCVA would 
> be a big impact.
>  
> Best.
>  
> Bruce Verhei 
> 
> On Apr 23, 2019, at 08:01, Ed Kramer <[email protected]> wrote:
> 
> Steve, you don’t mention the edition of 13 you’re working with, but I’m 
> looking in the ’16.
>  
> 23.4.4.2.5  is a sub-section of 23.4.4.2 “Density/Area Method”.  The section 
> above that is 23.4.4.1.1 “Room Design Method”.  I don’t see any similar 
> requirement in that section.  I’d argue that 23.4.4.2.5 doesn’t apply to the 
> room design method.  But some days I just feel like arguing.  J
>  
> Ed K
> Bamford Fire
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Prahl, Craig/GVL
> Sent: Tuesday, April 23, 2019 7:33 AM
> To: [email protected]
> Subject: RE: Intent of 23.4.4.2.5
>  
> I feel your pain.  This additional flow rate added to a small room has never 
> made any sense and I’d love to understand the logic of being forced to flow 
> 1,950 gpm into a room that is only required to deliver 150 gpm.   
>  
> Is there any actual benefit to this exercise?  
>  
> It’s amazing how buildings were assumed adequately protected when all that 
> was used was the pipe schedule method.  
>  
>  
> Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
> [email protected] | www.jacobs.com
> 1041 East Butler Road   Greenville, South Carolina  29606
>  
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Steve Leyton
> Sent: Monday, April 22, 2019 6:19 PM
> To: [email protected]
> Subject: [EXTERNAL] Intent of 23.4.4.2.5
>  
> We have a building with fire rated and secure compartments that are less than 
> the NFPA 13 minimum design areas so we have calculated those areas using the 
> room design method where the compartments comply.   Two are fire protected 
> with preaction sprinklers and 23.4.4.2.5 seems to imply that where a design 
> area is flowing less than what the density would be across the minimum 
> required design area, then a “kicker” needs to be added to raise the flow 
> rate to that figure.   Since we’re in Light Hazard and the design area is 
> only about 1,000 sq. ft., we’re flowing about 150 GPM.    But they’re coming 
> after us for 1,500 x 1.3 = 1,950 saying the required flow rate is 195.   If 
> it’s LH, we can downward adjust and the demand drops to 117 which we satisfy. 
>   In all my years I’ve never had this section thrown at us so could use any 
> help or opinion regarding exactly how this section should be applied.
>  
> <image001.jpg>
>  
>  
>  
> 
> NOTICE - This communication may contain confidential and privileged 
> information that is for the sole use of the intended recipient. Any viewing, 
> copying or distribution of, or reliance on this message by unintended 
> recipients is strictly prohibited. If you have received this message in 
> error, please notify us immediately by replying to the message and deleting 
> it from your computer.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org