I’m sure some of you have dealt with these Captive Aire / Piranha systems.
Basically they are hood systems that connect to the sprinkler system.  The
one I have a data sheet for has an operating pressure of 32-70 psi and flows
vary depending on # of nozzles.  How do those of you dealing with these
handle them?  The supplier will not do any calculations for the system.  My
question is, do we treat these like a “rack” system and balance the hood
systems to the overhead?  If I have a kitchen with 3 of these, do I figure
0, 1, 2 or 3 flowing simultaneously with the overhead.  As you can imagine,
a standard sprinkler in the kitchen is ±10 psi.  Now, if we have to treat
this like a rack system and balance at the junction point, this 30 psi for
the Piranha system will significantly over-discharge the sprinklers leading
to a much larger kitchen demand.  These often seem to be brought up toward
the end of the project leaving everyone scrambling.

 

What has the collective group been doing with these things?

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com

 

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low
price is forgotten.”

 

 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • Captive Aire Syste... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
    • RE: [EXTERNAL... Kyle.Montgomery via Sprinklerforum
      • RE: [EXTE... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
    • Re: Captive A... Bruce Verhei via Sprinklerforum
      • RE: Capti... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
        • Re: C... Matthew J Willis via Sprinklerforum
        • RE: C... Jonathan Mote via Sprinklerforum
          • R... Matthew J Willis via Sprinklerforum
            • ... Ron Greenman via Sprinklerforum
              • ... David Williams via Sprinklerforum
                • ... Matthew J Willis via Sprinklerforum

Reply via email to