I think “for the building being calculated” doesn’t take into account the 
potential arrangement of a single water line supplying domestic and fire 
protection to multiple buildings.    If I was the AHJ, I would require the 
fixture load allowance of both buildings to be added to the sprinkler demand of 
the subject building for that portion of the piping that is common to both 
buildings.   So if you’re coming in from a meter to the main building and call 
that Section A, then you have Section B going to the Satellite building, I 
would calculate Satellite sprinkler demand + Satellite domestic allowance in 
Section B, then at the point where the line branches off to the main building I 
would add the Main building plumbing allowance so that Section A includes 
Satellite sprinkler demand plus Satellite domestic + Main Building  domestic.

I hope that makes sense.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of J H via Sprinklerforum
Sent: Monday, September 09, 2019 3:17 PM
To: [email protected]
Cc: J H
Subject: 13R Fixture Units for Multiple Buildings

I've got a Bed & Breakfast (sprinklered per 13R) that is building a second 
detached suite which is to likewise be sprinklered to 13R. The existing yard 
line supplies both the domestic and fire demands for the existing building and 
the new building is planned to also tap into this yard line.

Question: In determining the fixture units for the new building would we also 
have to account for the existing building's fixture units when calculating back 
to the city tap?

13R states: "9.6* Domestic Demand  Domestic demand for the building being 
calculated shall be included as part of the overall system demand for systems 
with common domestic/fire mains where no provisions are made to prevent 
thedomestic waterflow upon sprinkler system activation."

I think the keywords are "for the building being calculated" and we would not 
have to account for anything else but I'm also thinking that if the intent is 
to account for water losses due to domestic usage and we are daisy chaining off 
of a relatively small, private, water line that it would be wise to account for 
these losses.

Any thoughts?

JH